I've tried adding an external sensor but there is no specific selection for the 9512 (just a TS100).
(CID:96043592)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:58 AM . Last Modified: 2024-04-10 12:01 AM
Hi Graham
The 320E is a version 2 device so Version 3 sensors are not compatible, the TS100 is the temperature sensor, HS100 Humidity sensor, FD100 Fluid sensor. There are also Dry contact sensors and 0-5v sensors.
If you need any we still stock them, Ecl-ips.com.
Regards
Aaron
(CID:96043594)