Inform UPS Monitoring

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Inform UPS Monitoring
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

0 Likes
5
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

Inform UPS Monitoring

Dear Team,

 

Please find attached pictures sent to me by manufacturer on the Inform UPS intelligence.

 

Kindly am not sure how best to go about monitoring this UPS, I am thinking of using NetBotz but am not sure. Any ideas?

Regards,

Felix

(CID:102924349)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

0 Likes
3
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

Hi Felix,

 

RS488 is a modbus communications option so I'm assuming the note about RS232 is also for Modbus.  The device also notes SNMP as an option. Although we do not have an option to monitor a serial modbus device, there is an option to monitor a modbus device using modbus over IP. This would require a gateway such as the TSXETG100. From what I can see that gateway only supports RS232 or RS485 but not RS488. To use these protocols, you would probably want to use the StruxureWare Data Center Expert software. 

 

The other image you posted was a simple normally open or normally closed connection. NetBotz would be the option here. You can use a dry contact cable to monitor the change in state for this  normally open or normally closed connection. If the system has multiple dry contacts, you simply connect multiple dry contact cables. If the device only has a single physical output, I'm assuming that all events on the device will use this connection and the NetBotz device will not be able to tell you what speific alert is happening, just that the device is in alert as sensed by the contact.

 

How any of this is set up on the device itself would be something you'd have to work out with the manufacturer.


Steve.

 

 

(CID:102924355)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

0 Likes
3
1435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

Hi Felix,

 

RS488 is a modbus communications option so I'm assuming the note about RS232 is also for Modbus.  The device also notes SNMP as an option. Although we do not have an option to monitor a serial modbus device, there is an option to monitor a modbus device using modbus over IP. This would require a gateway such as the TSXETG100. From what I can see that gateway only supports RS232 or RS485 but not RS488. To use these protocols, you would probably want to use the StruxureWare Data Center Expert software. 

 

The other image you posted was a simple normally open or normally closed connection. NetBotz would be the option here. You can use a dry contact cable to monitor the change in state for this  normally open or normally closed connection. If the system has multiple dry contacts, you simply connect multiple dry contact cables. If the device only has a single physical output, I'm assuming that all events on the device will use this connection and the NetBotz device will not be able to tell you what speific alert is happening, just that the device is in alert as sensed by the contact.

 

How any of this is set up on the device itself would be something you'd have to work out with the manufacturer.


Steve.

 

 

(CID:102924355)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

In response to DCIM_Support
0 Likes
0
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

Hi Steve, Thanks a lot, I shall update on the progress. Regards, Felix

(CID:102924364)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

In response to DCIM_Support
0 Likes
0
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

Hi Steve, The manufacturer has advised that Rs488 and Rs232 are not for modbus, they are for serial communication. The UPS apparenty doesn't have any modbus connection. I guess now we have NetBotz as the option left, but am not familiar on how to do this. Regards, Felix

(CID:102924387)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

In response to DCIM_Support
0 Likes
0
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2024-04-09 03:10 AM

Hi Felix, They did note SNMP in the initial screenshots as well. If that too is not something available then yes, dry contacts with NetBotz would be the way to go. Steve

(CID:102924483)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2023-10-31 11:09 PM

0 Likes
0
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:25 PM . Last Modified: ‎2023-10-31 11:09 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore