Posted: 2021-07-05 06:47 AM
Dear Community,
I have a few questions regarding tenant login in web client:
1. Is the floor layout is meant to show in in whole? Compare to the previous version of Colo feature where tenant get to see their own cage layout only?
* The squared location is the tenant's cage.
BR
TJ
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-06 02:29 AM
Hi TJ,
That's correct in latest version(s) of ITA, tenant may access the area/equipment based on permissions but may also see the reset of the 'greyed out' floor area (with no info/details).
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-06 01:22 AM . Last Modified: 2021-07-06 08:37 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-06 01:22 AM . Last Modified: 2021-07-06 08:37 PM
Upgrading from DCO 8.x to IT Advisor · How to download Data Center Expert and IT in a virtual environment · Installing ITA in a location without public Internet access ITA system requirements for on-premises installations Colo and tenant Desktop client login issue possible after updating to ITA 9.1.9.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-06 02:29 AM
Hi TJ,
That's correct in latest version(s) of ITA, tenant may access the area/equipment based on permissions but may also see the reset of the 'greyed out' floor area (with no info/details).
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-06 02:57 AM
Hi Jones,
Going forward please open a new 'case' when posting a question.
If the data needs to be downloaded from the Internet (such as installation files for ITA), then you would need to use a laptop or workstation that has Internet access. Download the file(s) and then transfer to a storage driver and then make it available in your closed network environment.
Currently the installation file(s) for ITA (including the latest 9.2.0 release) available as:
offline installer (such as EcoStruxureITAdvisor9.2.0-offline.iso)
and online installer (such as EcoStruxureITAdvisor9.2.0.iso)
So, if there is no Internet access during the installation then use the offline installer.
Additional info:
a more general description of upgrading from DCO 8.x to ITA:
https://helpcenter.ecostruxureit.com/hc/en-us/articles/360009560538-Upgrading-from-DCO-8-x-to-IT-Adv...
migrating/upgrading from DCO to ITA:
https://helpcenter.ecostruxureit.com/hc/en-us/articles/360006367378-Migrating-from-DCO-to-ITA
if you are upgrading from Colo to ITA, then please see this article as well:
https://helpcenter.ecostruxureit.com/hc/en-us/articles/360036670893-Can-I-upgrade-to-ITA-on-premise-...
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 05:18 PM
Hi Jef,
Thanks for the clarification. Another question is that, are we able to set "customer" properties for space/room TH sensors? The tenant wishes to view the space/room sensors under their cage. I understand tenants are able to view the TH sensors installed inside the racks.
BR,
TJ
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-14 11:43 PM
Hi TJ,
You are very welcome. That's correct, tenant can view the associated temperature/humidity sensors, but we cannot set custom properties on them. In general, custom properties can be defined/set on ITA models (and not on the external systems items such as T/H sensors).
Kind regards,
Jef