Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

IT Security for Netbotz and other APC Datacenter Equipment

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • IT Security for Netbotz and other APC Datacenter Equipment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

0 Likes
4
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

IT Security for Netbotz and other APC Datacenter Equipment

Our customer has Netbotz 200 at a remote datacenter connected to DCE at main datacenter over corporate network . After their IT security audit it was raised the the Netbotz 200 has open ftp ports and the password is week. The netbotz is connected to Data Center Expert. How best can we guarantee the security of the APC equipment and DCE on the network.

 

They are concerned about preventing from malicious code upload or from other people who are ware of the password from accessing the netbotz via ftp (or other protocols  over the corporate network) and make harmful changes. Is netbotz ftp read-only, or is there a way to make it read only without affecting the connection with DCE.

 

Can I have a separate user for connecting to DCE and onother for http or https.

 

What are the best IT security measures we can implement for all APC and Schneider Electric (UPSes, Inrows, PDUs etc) as they support network critical systems

 

I saw these commands are available in ftp 

rename, delete, mdelete

(CID:143757615)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

0 Likes
2
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

Hi Cleopas,

 

If your customer feels that their password is weak, they should change their password. The FTP password is the admin password on those NetBotz 200 devices. If they do not like FTP, they can also disable FTP and use SCP. 

The same passwords for administrators can also be used for ftp, you can't change that. My suggestion would be to limit access to the NetBotz appliance , UPS, etc by only allowing them read only access. 

 

Thanks,

Steve

(CID:143757660)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

In response to DCIM_Support
0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

How do make the units read-only, I would like to maintain a connection with the DCE at main datacenter.

 

Can admin make harmful changes like delete using FTP?

 

Is FTP required by DCE? If not I may need to disable it.

(CID:143757926)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

In response to DCIM_Support
0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2024-04-03 02:43 AM

Hi Cleopas,

When you discover a device, DCE needs FTP (or scp) to pull an alert definition file from the device. When configuring a device through DCE, the same protocol(s) are used to pull / push the configuration file. Finally, the same protocol is used to push a firmware upgrade. These must be enabled (either FTP or SCP) for full compatibility with DCE.

 

What are you worried about deleting? You can't delete the firmware but you can delete the event log for instance. This would be similar access as if you had admin access to the web page.

For security purposes, you can configure 3 levels of users on the device itself. Here's the old firmware on a NetBotz 200:

Here's what it looks like on the newer cards:

 

If you do not want someone to have the user name and password to be allowed to FTP to the card directly, provide them with the read only user name and password.

If you're using DCE, You can also give people granular access to device groups:

You can specify device launch settings for each device so that when they double click a device in DCE, they only get the type of access provided by the user name and password used:

 

 

If you do not have the proper access to DCE, you will also not have access to see the device file transfer settings which is where the FTP or SCP settings are held for the purposes that I mentioned in the beginning:

So an admin will be able to see these settings:

so if I were to give you view and control access over devices:

You wouldn't even have the "device" menu required to access these user names and passwords:

 

Steve

 

 

(CID:143758723)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2023-10-22 02:40 AM

0 Likes
0
1083
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:15 PM . Last Modified: ‎2023-10-22 02:40 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore