Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

IT Gateway Discovery - No Device Found

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • IT Gateway Discovery - No Device Found
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
CSelf
CSelf
Explorer

Posted: ‎2024-08-14 08:43 PM

0 Likes
3
2882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-14 08:43 PM

IT Gateway Discovery - No Device Found

We are currently upgrading from DCE, during my initial testing of EcoStruxure IT I installed the Gateway on my laptop and had no issues discovering our current APC devices.  Since we are a 100% cloud based environment, I created a Windows Server 2019 Azure VM to host the Gateway.  I understand this is not recommended but have seen posts from folks with similar setups. 

The Gateway has been installed with the same settings I used during testing but no devices are found when running a discovery.  I can ping each of the IP's of the devices and even access their web pages from the VM and I've verified the necessary ports are open on the server as well as the firewall. 

Are there any specific settings on the devices that would block a discovery?

Anywhere I could specify the IP of the Gateway?

 

Labels
  • Labels:
  • IT Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-08-20 06:15 AM

In response to CSelf
0 Likes
0
2822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-20 06:15 AM

Hi @CSelf,

 

If no traffic is coming back through the firewall, you will need to look and see what is occurring either on the device (should be processing the request) or on the network between the firewall and the device.  If this is happening to more than 1 device, the issue is likely something on the network that is blocking traffic, such as a layer 3 switch with ACLs or something that is blocking the outbound traffic (response) from the NMC back to the software.

 

A way to test if the device is responding to requests would be to connect your computer directly to the network port of the device and create an ad-hoc 1-to-1 connection.  You will need to assign an IP address that is on the same network as the device.  It is recommended to use an IP that is one number off from the IP of the device, the same subnet, and a gateway of the end-device so that traffic will flow correctly.

NOTE: Sometimes a Wi-fi adapter needs to be disabled or Wi-Fi turned off to get the communication to work properly.

 

You can then run the SNMPwalk software to see if you get a response from the device.  If you do, the issue is network related.  If you don't, either it is with the 1-to-1 network setup, polling software, or the device itself (not likely if it is affecting multiple devices).

 

Kind Regards,

Cory

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-08-16 12:21 PM

1 Like
0
2870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-16 12:21 PM

Hello @CSelf,

 

I always recommend by starting with the NMC Event log to see if there are unauthorized attempts from your computers (gateway's) IP address.  The event log can be accessed from the NMC interface by going to: Logs > Events > Log.

Since these devices were already configured and communicating to DCE, most of the SNMP settings on the device should be correct.  In most APC SNMP interfaces this should be under: Configuration > Network > SNMPv1 > Access Control

Cory_McDonald_0-1723835703779.png

 

 

If there is an NMS IP/Hostname you will need to update that value to be the Gateway IP Address (communication will be lost to DCE) or update it to be a more broad entry such as 0.0.0.0 or 10.10.10.0 depending on what DCE's IP address is and the Gateway's IP Address is.

Cory_McDonald_1-1723835776670.png

 

If SNMPv3 is being used the menu option would be under: Configuration > Network > SNMPv3 > Access Control

Cory_McDonald_2-1723835830634.png

 

As long as the same protocol is being used to Discover in the gateway that was configured to be used in DCE, the devices should discover.

 

The usual other culprit would be network.  You can attempt to do an SNMPwalk from your computer (where the gateway is installed) using the following utility: https://community.se.com/t5/Troubleshooting/How-to-create-a-device-walk-file-for-EcoStruxure-IT-Gate...

 

If the walk is successful then the communication channel is open and the discovery issue would fall to a configuration within ITE for the discovery.  Double-check your discovery settings or run another discovery using the same settings you used within the utility.

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

CSelf
CSelf
Explorer

Posted: ‎2024-08-16 09:47 PM

0 Likes
1
2831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-16 09:47 PM

Hi Cory,

Thanks for your response. 

There are a few "Detected an unauthorized user attempting to access the SNMP interface from.." with the IP of my endpoint, not the server running the discovery, is this normal?  Occasionally when I tweak the SNMP settings on one of the devices I'm testing with I'll see the same SNMP error in the logs with the IP of the DCE, it resolves itself when I revert the changes, the error with my endpoint IP is consistent.  I've verified all of the SNMP settings are the same on the devices as well as the gateway.

I downloaded and ran the device walker utility on the server, each device IP times out, I've tried multiple command variations including adding the read and write strings and specifying the port.

CSelf_0-1723869363677.png

I've also checked our Palo firewall logs, traffic is getting out to the APC device but no packets are being sent back.  Other APC traffic (SMTP, SSL) passes through the FW with no issues. 

Thanks again for the great response.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2024-08-20 06:15 AM

In response to CSelf
0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-20 06:15 AM

Hi @CSelf,

 

If no traffic is coming back through the firewall, you will need to look and see what is occurring either on the device (should be processing the request) or on the network between the firewall and the device.  If this is happening to more than 1 device, the issue is likely something on the network that is blocking traffic, such as a layer 3 switch with ACLs or something that is blocking the outbound traffic (response) from the NMC back to the software.

 

A way to test if the device is responding to requests would be to connect your computer directly to the network port of the device and create an ad-hoc 1-to-1 connection.  You will need to assign an IP address that is on the same network as the device.  It is recommended to use an IP that is one number off from the IP of the device, the same subnet, and a gateway of the end-device so that traffic will flow correctly.

NOTE: Sometimes a Wi-fi adapter needs to be disabled or Wi-Fi turned off to get the communication to work properly.

 

You can then run the SNMPwalk software to see if you get a response from the device.  If you do, the issue is network related.  If you don't, either it is with the 1-to-1 network setup, polling software, or the device itself (not likely if it is affecting multiple devices).

 

Kind Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore