How to create a device walk file for EcoStruxure IT Gateway and Data Center Expert

Troubleshooting

How to troubleshoot and solve issues configuring the EcoStruxure IT Gateway

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Gateway
  • Troubleshooting
  • How to create a device walk file for EcoStruxure IT Gateway and Data Center Expert
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • How to troubleshoot the Gateway connection to EcoS...
  • How to troubleshoot SNMP communication issues in t...
  • How to solve the cloud connectivity untrusted SSL ...
  • How to set up the Gateway proxy settings
  • How to restart the Gateway Service
  • How to replace the self-signed SSL certificate in ...
  • How to replace a device in EcoStruxure IT Gateway
  • How to disconnect or reconnect a Gateway from EcoS...
  • How to create a device walk file for EcoStruxure I...
  • How to allow a targeted read for Device Support
  • Gathering Gateway logs for troubleshooting
  • Gateway restore fails on some non-English locales
  • Gateway appliance network problems due to bad imag...
  • Gateway Device Communication Alert
  • Galaxy UPS is offline after updating the Gateway
  • Device serial numbers and unique identifiers
  • Device is offline after replacement or RMA
  • Device discover fails - SNMP is disabled by defaul...
  • Cannot discover Redfish devices in Gateway
  • Cannot discover NetBotz devices in Gateway
  • Web server port 443 is being used by another appli...
  • Troubleshooting issues connecting your Gateway to ...
  • Troubleshooting Gateway device discovery failure
  • SNMP walks, Modbus polls, and Redfish discoveries
  • NetBotz devices appear in the list of unknown devi...
  • NetBotz 4.x discovery issue when Gateway proxy set...
  • My device name didn't update in the Gateway after ...
  • My device is not responding - Gateway 1.4.0
  • How to troubleshoot the Gateway connection to EcoS...
  • How to troubleshoot SNMP communication issues in t...
  • How to solve the cloud connectivity untrusted SSL ...
  • How to set up the Gateway proxy settings
  • How to restart the Gateway Service
  • How to replace the self-signed SSL certificate in ...
  • How to replace a device in EcoStruxure IT Gateway
  • How to disconnect or reconnect a Gateway from EcoS...
  • How to create a device walk file for EcoStruxure I...
  • How to allow a targeted read for Device Support
  • Gathering Gateway logs for troubleshooting
  • Gateway restore fails on some non-English locales
  • Gateway appliance network problems due to bad imag...
  • Gateway Device Communication Alert
  • Galaxy UPS is offline after updating the Gateway
  • Device serial numbers and unique identifiers
  • Device is offline after replacement or RMA
  • Device discover fails - SNMP is disabled by defaul...
  • Cannot discover Redfish devices in Gateway
  • Cannot discover NetBotz devices in Gateway
  • Web server port 443 is being used by another appli...
  • Troubleshooting issues connecting your Gateway to ...
  • Troubleshooting Gateway device discovery failure
  • SNMP walks, Modbus polls, and Redfish discoveries
  • NetBotz devices appear in the list of unknown devi...
  • NetBotz 4.x discovery issue when Gateway proxy set...
  • My device name didn't update in the Gateway after ...
  • My device is not responding - Gateway 1.4.0

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Troubleshooting
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
9532 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to create a device walk file for EcoStruxure IT Gateway and Data Center Expert

Picard EcoStruxureIT
‎2020-05-28 03:09 AM

Last Updated: Sisko JLehr Sisko ‎2025-06-20 09:17 AM

This tool can walk SNMP1, SNMP3, Modbus, Redfish, NetBotz, and FTP devices, gathering current values or files to facilitate DDF development or debugging for Data Center Expert or EcoStruxure IT Gateway.

 

Specific information about how to create a walk file for different DCE versions is here.

 

Modbus.org announced it is expunging all occurrences of inappropriate language of the query and response paradigm of Modbus communications. This tool was updated to comply as of version 1.9.1. More...

 

Requirements

 

  • Windows 10+ or Windows Server 2012+
  • Admin access to Command Line or Windows PowerShell

 

Getting started

 

1. Unzip the file walker_version_Windows.zip

2. Navigate to the folder you unzipped in step 1.  There should be a file called "walk.bat" in the folder.

3. Right click the file and click Open.

 

How to run your first command

Note: In Gateway 2.x, double dashes replaced single dashes in commands.

 

The general usage is:

<protocol> --ip <ip> <options>

 

Example: snmp --ip 192.169.0.10

 

Note: To read more about each command while you run the program, type help followed by the command you need help for. Example: help snmpv3

 

idea_icon_360009259237.pngidea_icon_360009259237.png There are several example commands below. Make sure to follow the structure carefully.

 

Running a command generates a walk file that is named using the IP address and a *.walk, *.json, *.txt", or *.xml extension. The file is saved to the folder where you ran the .bat script. If you are running a walk that retrieves raw files, such as FTP, these are saved as files.zip.

 

Example output: 192.169.0.10.xml
Example with file retrieval: 192.169.0.10.txt and files.zip

 

Troubleshooting

 

If you're having trouble connecting to a physical device, check with your network administrator to confirm that the device is enabled for the protocol and login credentials (if applicable) you are using to connect.

 

Device walks can take a long time to complete. A walk usually completes within 20 minutes for a slow connection.

 

If your walk fails to complete, it might be worth taking a break. Many protocols struggle to handle excessive repeated requests. If the walk seems to be hanging, try waiting a few hours and try again; this gives the device time to discard any old sessions and start accepting new ones. If the walk still fails, contact support for assistance.

 

If your Modbus poll output file does not get generated and you are running the walk.bat file as an administrator, try closing the program, right-click "walk.bat", and select "Open" (not "Run as administrator").

Usage details

 

SNMP V1

 

Defaults

 

-- ip: REQUIRED

-- port: 161

-- file: <ip>.walk
-- read: public
-- write: private
-- retries: 2
-- timeout: 5

-- enableBulkRequest: false

 

Examples

 

snmp --ip 192.169.0.10

snmp --ip 192.169.0.10 -port 8161

snmp --ip 192.169.0.10 -read pass

 

SNMP V3

 

Argument valid values

 

-- authType: MD5, SHA
-- encType: DES, DES3, AES128, AES192, AES256

 

Defaults

 

-- ip: REQUIRED

-- port: 161

-- file: <ip>.walk

-- username: REQUIRED

-- authType:

-- authPassword:

-- encType:

-- encPassword:

-- retries: 2

-- timeout: 5

-- enableBulkRequest: false

 

Examples

 

snmpv3 --ip 192.169.0.10 --port 161 --username XXXX --authType MD5 --authPassword XXXX --encType DES --encPassword XXXX

 

snmpv3 --ip 192.169.0.10 --port 161 --username XXXX --authType SHA --authPassword XXXX --encType AES128 --encPassword XXXX 

 

snmpv3 --ip 192.169.0.10 --port 161 --username XXXX 

 

snmpv3 --ip 192.169.0.10 --port 161 --username XXXX --authType SHA --authPassword XXXX 

 

Modbus

 

This requires a separate text file specifying which registers to read. See input.txt for formatting and examples.

 

WARNING: Excessive Modbus requests can overwhelm the device. Keep the number of selected registers as small as possible.

 

NOTE: The walker will output an XML file with the naming convention {ip_address}-{server_id}.xml (e.g., 12.34.56.789-1.xml). If this file does not get generated and you are running the walk.bat file as an administrator, try closing the program, right-click "walk.bat", and select "Open" (not "Run as administrator").

 

Defaults

 

-- <ip>: REQUIRED

-- port: 502

-- file:
-- server: 1
-- input: input.txt

-- maxReads: 100

-- walk: true

-- function:

-- start: 1

-- count:

-- print:

 

Examples

 

modbus --ip 192.169.0.10

 

modbus --ip 192.169.0.10 --port 5020 --server 2 --input registers.txt

 

Redfish

 

Defaults

 

-- ip: REQUIRED
-- port: 443
-- file: <ip>.json
-- username: REQUIRED
-- password: REQUIRED

 

Example

 

redfish --ip 192.168.0.10 --username user1 --password pass

 

NetBotz

 

Defaults

 

-- ip: REQUIRED
-- port: 80
-- file: <ip>.json
-- username: 
-- password: 

-- useSSL: false

 

Examples

 

netbotz --ip 192.168.0.10 --username user1 --password pass

 

netbotz --ip 192.168.0.10 --username user1 --password pass --useSSL

 

FTP

 

Defaults

 

-- ip: REQUIRED
-- port: 21
-- file: <ip>.json
-- username: 
-- password:
-- walk: true
-- download_file:

 

Example

 

ftp --ip 10.155.55.55 --username apc --password apc

Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore