I cannot connect to the IT Gateway

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • I cannot connect to the IT Gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
128
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
huynhngochoi
Lieutenant | EcoXpert Master huynhngochoi Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-12-10 08:55 PM . Last Modified: ‎2020-12-10 10:44 PM

0 Likes
6
3268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-10 08:55 PM . Last Modified: ‎2020-12-10 10:44 PM

I cannot connect to the IT Gateway

I cannot connect to the IT Gateway
I followed your instructions,

 
 

Capture.PNG

But I can't connect to Webmin at 192.168.0.1:10000

 

 

 

 

 

Labels
  • Labels:
  • Data Center Operation
  • DCIM Support
  • IT Advisor
  • IT Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BjarkeFenger
Lieutenant JG BjarkeFenger Lieutenant JG
Lieutenant JG

Posted: ‎2020-12-17 11:02 AM

In response to huynhngochoi
0 Likes
0
3139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-17 11:02 AM

Hi Ngoc Hoi

 

This line of devices device have had some problems with software where the network stack does not initialize properly. 

You need to reach out to our support team who are aware of this problem and can work with you to either change the impacted unit, or work with you to reinstall the base image on the device.

 

Bjarke Fenger

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BjarkeFenger
Lieutenant JG BjarkeFenger Lieutenant JG
Lieutenant JG

Posted: ‎2020-12-13 11:19 PM

0 Likes
5
3214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-13 11:19 PM

Hi @huynhngochoi 

 

Are you using a Schneider Gateway Appliance as the Intel NUC or Dell Server?

If no, which type of server are you running the gateway on?

 

/Bjarke

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

huynhngochoi
Lieutenant | EcoXpert Master huynhngochoi Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-12-13 11:37 PM

In response to BjarkeFenger
0 Likes
4
3209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-13 11:37 PM

Hi @BjarkeFenger 

I do not quite understand what you mean. I just follow the instructions shown in the picture that I posted to access Webmin. But it doesn't work. Here is what I did.

image5.jpegimage1.jpegimage0.jpegimage2.jpeg

 

I also tried to set my computer receive a DHCP address but it also failed.

 

NgocHoi

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

huynhngochoi
Lieutenant | EcoXpert Master huynhngochoi Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-12-15 05:42 PM

In response to huynhngochoi
0 Likes
0
3186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-15 05:42 PM

Hi,

Because this new product so I can not find many documents, as well as the experience of everyone.

So anyone know this error please tell me. Please help me.

Thank you very much.

NgocHoi

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BjarkeFenger
Lieutenant JG BjarkeFenger Lieutenant JG
Lieutenant JG

Posted: ‎2020-12-17 02:20 AM

In response to huynhngochoi
0 Likes
2
3163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-17 02:20 AM

Hi huynhngochoi

 

I can see that you are setting a static IP on their laptop, so I suggests the DHCP isnt running properly.

Can you send us the date code from the shipping box the Gateway came in? That would help us to see which unit and version you are using.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

huynhngochoi
Lieutenant | EcoXpert Master huynhngochoi Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-12-17 05:00 AM . Last Modified: ‎2020-12-17 05:01 AM

In response to BjarkeFenger
0 Likes
1
3159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-17 05:00 AM . Last Modified: ‎2020-12-17 05:01 AM

Hi @BjarkeFenger,

I sent the pictures you requested.

image.jpg

Ngoc Hoi

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BjarkeFenger
Lieutenant JG BjarkeFenger Lieutenant JG
Lieutenant JG

Posted: ‎2020-12-17 11:02 AM

In response to huynhngochoi
0 Likes
0
3140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-17 11:02 AM

Hi Ngoc Hoi

 

This line of devices device have had some problems with software where the network stack does not initialize properly. 

You need to reach out to our support team who are aware of this problem and can work with you to either change the impacted unit, or work with you to reinstall the base image on the device.

 

Bjarke Fenger

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore