Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to set Location of devices in EcoStruxure IT

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How to set Location of devices in EcoStruxure IT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

0 Likes
4
2019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

How to set Location of devices in EcoStruxure IT

Hi,

We have 2 DCE servers connected to the EcoStruxure IT service. In the portal we have 2 locations listed, which correspond to the 2 locations the DCE servers are located at.

Previously any equipment in the DCE server has been associated with the relevant site.

However we have added some new equipment in and it is now appearing under "All Locations". I have been unable to find out where (if it is even possible) to change/associate the location of the device?

Has anyone any ideas or come across this?

Thanks

Matt

(CID:131959542)

Labels
  • Labels:
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

0 Likes
2
2019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

Dear Matt Wagner,

From your question:

However we have added some new equipment in and it is now appearing under "All Locations".

At the moment it really works like this: the logic of managing the location hierarchy of devices on the app.ecostruxureit.com/manage portal has changed, for example, read this Location hierarchy does not match DCE device groups:

Device groups in Data Center Expert and the location hierarchy on app.ecostruxureit.com/manage are completely separate. You maintain the location hierarchy on app.ecostruxureit.com/manage.

Therefore, once you have added a new device(s) in DCE-server or EcoStruxure IT Gateway, you must create on portal app.ecostruxureit.com/manage your own hierarchy of locations (not to be confused with the location of the DCE-server or EcoStruxure IT Gateway) and place the new device(s) in the correct locations.

From my own practical experience I can confirm, that this new way of managing the hierarchy of device(s) locations and DCE-servers is really very correct and convenient. Since very often the same DCE-server monitors devices from different locations of sites. That's why the developers and designers of EcoStruxure IT have separated the location of the DCE-server (or several DCE-servers) and the location of all other devices.

Unfortunately, I could not find any instructions or video on the new way to configure the hierarchy of device locations on portal app.ecostruxureit.com/manage. Therefore, below is my brief instruction in the screenshots.

  • Login to the portal app.ecostruxureit.com/manage and click on link All location:
  • Next click on link Manage...:
  • Click the Add site... link to add a new site location or Add room... to add a new room for the site:
  • And add new site location:
  • Or add new room for the site:
  • After that, all your new device(s) without location (i.e. "All Locations") can be very conveniently associated with your new site(s) and room(s) on the portal app.ecostruxureit.com/manage.

  • In addition, for each individual DCE-server or EcoStruxure IT Gateway, you can separately associate users for priority calling:

I hope this helps you.

If you have any further questions, please ask.

With respect.

(CID:131959804)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

0 Likes
2
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

Dear Matt Wagner,

From your question:

However we have added some new equipment in and it is now appearing under "All Locations".

At the moment it really works like this: the logic of managing the location hierarchy of devices on the app.ecostruxureit.com/manage portal has changed, for example, read this Location hierarchy does not match DCE device groups:

Device groups in Data Center Expert and the location hierarchy on app.ecostruxureit.com/manage are completely separate. You maintain the location hierarchy on app.ecostruxureit.com/manage.

Therefore, once you have added a new device(s) in DCE-server or EcoStruxure IT Gateway, you must create on portal app.ecostruxureit.com/manage your own hierarchy of locations (not to be confused with the location of the DCE-server or EcoStruxure IT Gateway) and place the new device(s) in the correct locations.

From my own practical experience I can confirm, that this new way of managing the hierarchy of device(s) locations and DCE-servers is really very correct and convenient. Since very often the same DCE-server monitors devices from different locations of sites. That's why the developers and designers of EcoStruxure IT have separated the location of the DCE-server (or several DCE-servers) and the location of all other devices.

Unfortunately, I could not find any instructions or video on the new way to configure the hierarchy of device locations on portal app.ecostruxureit.com/manage. Therefore, below is my brief instruction in the screenshots.

  • Login to the portal app.ecostruxureit.com/manage and click on link All location:
  • Next click on link Manage...:
  • Click the Add site... link to add a new site location or Add room... to add a new room for the site:
  • And add new site location:
  • Or add new room for the site:
  • After that, all your new device(s) without location (i.e. "All Locations") can be very conveniently associated with your new site(s) and room(s) on the portal app.ecostruxureit.com/manage.

  • In addition, for each individual DCE-server or EcoStruxure IT Gateway, you can separately associate users for priority calling:

I hope this helps you.

If you have any further questions, please ask.

With respect.

(CID:131959804)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

In response to DCIM_Support
0 Likes
0
2019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

Thank you, that's a very thorough explanation.

I think the step i am struggling with is this part "After that, all your new device(s) without location (i.e. "All Locations") can be very conveniently associated with your new site(s) and room(s) on the portal app.ecostruxureit.com/manage."

I've looked through the manage locations and device sections and cant actually see where you would associate them with a site/room?

Actually i've just figured it out, I needed to select the tick box next to a device, then the Actions menu appears where i can move it!

Thanks

Matt

(CID:131959829)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

In response to DCIM_Support
0 Likes
0
2019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2024-04-04 11:53 PM

Dear Matt Wagner,

This is correct, indeed, the device(s) must first be selected, and only then the action menu will appear 😀. In my screenshots I can not show this, because I do not have devices without location (i.e. "All Locations").

With respect.

(CID:131959850)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2023-10-22 02:34 AM

0 Likes
0
2019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:34 PM . Last Modified: ‎2023-10-22 02:34 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore