How can I get the NetBotz email alerts from DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How can I get the NetBotz email alerts from DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

0 Likes
5
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

How can I get the NetBotz email alerts from DCE

Hi,

     I have received alerts from NetBotz 570 to DCE but I didn't receive the Email alerts from DCE . DCE is configured properly and we receive the Email alerts from other devices expect NetBotz.

how can I get the NetBotz email alerts from DCE-7.2.7.

(CID:105467179)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

0 Likes
2
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

Dear Ali,

As far as I know, we need to configure the Netbotz email Server settings in order to receive the email alert when an alarm occurs. 

The email configuration can be done either via DCE or through Netbotz Appliance Advance View Software. 

There is a K-base document(ID: FA226040) available which explains on how to Configure NetBotz appliances to send e-mails on an alert.

I hope that this helps. 

Regards,

Bala

(CID:105467200)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

In response to DCIM_Support
0 Likes
0
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

Bala's configuration options are correct, The configuration for e-mail will reside on the NetBotz appliance. This was the initial design since NetBotz Central so there would be no single point of failure. DCE can go down and the appliances will still alert on their own. This is also important as NetBotz has many ways to alert (relay outputs, modems, etc) that can't rely on DCE. Steve

(CID:105467233)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

In response to DCIM_Support
0 Likes
0
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

can any one share the email alerts setting on gmail server , i already sett all in correct way to get email of alerts from netbotz but i cant recv emails , but i am getting emails other then netbotz - from DCE. umair512@gmail.com

email .jpg

(CID:110006100)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

0 Likes
0
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2024-04-09 12:54 AM

I think this is one of the biggest downfalls of DCE, there are pro's and cons for having the emails configured in the device, but I find that in our organization the administration overhead to do so at the appliance level is prohibitive. Given this is the case we only use the Netbotz200 devices so that we can have a centrally managed and backed up system. 

(CID:105467265)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2023-10-31 11:00 PM

0 Likes
0
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:29 AM . Last Modified: ‎2023-10-31 11:00 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore