Hi Felix,
You will need to enable it through webservices. The customer feature has been designed so it can integrate to a 3rd. party customer database. So customer relations can be maintained in the 3rd. party system, but relevant information will be passed to Data Center Operation. If you don't use a 3rd. party customer database can you also add induvidual users using for instance SoapUI. Please see information about adding colo customers.
Link: http://dcimsupport.apc.com/display/DCIMDEVELOPER/CustomerWebService
Thanks
Jesper
(CID:89555524)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 08:27 AM . Last Modified: 2024-04-10 01:30 AM
Hi Felix,
You will need to enable it through webservices. The customer feature has been designed so it can integrate to a 3rd. party customer database. So customer relations can be maintained in the 3rd. party system, but relevant information will be passed to Data Center Operation. If you don't use a 3rd. party customer database can you also add induvidual users using for instance SoapUI. Please see information about adding colo customers.
Link: http://dcimsupport.apc.com/display/DCIMDEVELOPER/CustomerWebService
Thanks
Jesper
(CID:89555524)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 08:27 AM . Last Modified: 2023-10-31 11:00 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.