Fail to "Apply Firmware Udaptes..." via DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Fail to "Apply Firmware Udaptes..." via DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

0 Likes
6
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

Fail to "Apply Firmware Udaptes..." via DCE

Hi,

could you please help me to know for which reason "Apply Firmware Udaptes..." does not work via DCE?

error message: "Failed to update device: unable to transfer AOS 6.2.0."

more info:

DCE version 7.2.6

"StruxureWareDataCenterExpertFWCatalog.zip" loaded in DCE manually

Perhaps some trick/suggestion for "Device File Transfer Settings" ?

 

Thx&Brgds,

Massimo

(CID:94601618)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

Hi Massimo,

Like Scott stated, DCE uses either FTP or SCP to transfer the upgrade files from the DCE server to the network management card. Being that FTP/SCP is an administrator privilege, DCE would require the Administrator account credentials.  I would recommend the following 

  1. Verify that the Network Management Card(NMC) has FTP enabled
  2. Verify that you can FTP to the NMC via a command line from your PC
  3. Verify that DCE has the correct credentials. Please follow the path below to ensure credentials
    1. from within the DCE client, click on the Device drop down menu
    2. hoover the mouse of SNMP Device Communication Settings
    3. select Device File Transfer Settings. Within this window you will find all the credentials DCE will use to transfer a file from the appliance to the NMC.

 

Please let me know how you make out.

 

Thank You

Victor 

 

(CID:94601849)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

Hi Massimo, we will investigate it, thanks for sharing.

(CID:94601642)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

Hi Massimo, have you logged into the device and ensured that the FTP server is enabled? There also could be a firewall issue somewhere between DCE and the device on the specified port. By chance have you used the "APC SNMP Device Configuration" mechanism between DCE and this device or others on the same segment? The configuration mechanism also uses FTP and could rule out some of the issues that could cause what you're seeing.

(CID:94601732)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

Hi Scott, this mean that it is NOT possible to upgrade devices fw using the secure protocol as scp ?... this is a very important point... Brgds, Massimo

(CID:94601789)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

0 Likes
0
1513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 AM . Last Modified: ‎2024-04-10 12:43 AM

Hi Massimo,

Like Scott stated, DCE uses either FTP or SCP to transfer the upgrade files from the DCE server to the network management card. Being that FTP/SCP is an administrator privilege, DCE would require the Administrator account credentials.  I would recommend the following 

  1. Verify that the Network Management Card(NMC) has FTP enabled
  2. Verify that you can FTP to the NMC via a command line from your PC
  3. Verify that DCE has the correct credentials. Please follow the path below to ensure credentials
    1. from within the DCE client, click on the Device drop down menu
    2. hoover the mouse of SNMP Device Communication Settings
    3. select Device File Transfer Settings. Within this window you will find all the credentials DCE will use to transfer a file from the appliance to the NMC.

 

Please let me know how you make out.

 

Thank You

Victor 

 

(CID:94601849)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:55 AM . Last Modified: ‎2024-04-10 12:43 AM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:55 AM . Last Modified: ‎2024-04-10 12:43 AM

Hi Victor thanks for your input.

I've tried to enable FTP on NMCs and it worked only in one case ...

Do you have more suggestion about this ?

Brgds,

Massimo.

(CID:94602937)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:55 AM . Last Modified: ‎2023-10-31 10:58 PM

0 Likes
0
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:55 AM . Last Modified: ‎2023-10-31 10:58 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.