Email configuration Netbotz

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Email configuration Netbotz
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

0 Likes
5
2209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

Email configuration Netbotz

Hello everybody.

I am configuring some Netbotz appliances like 570 for example and sometimes when i put the informations about email server , i try to do the "send test email" but it shows like : unable to send test email. I did the whole steps that the Netbotz guide suggests  I reached good results but  last time, i put all the informations and the same message appears.All informations were correct but it didn´t work. Probably the Netbotz is not accessing the mail server , or there´s some SSL problem , i don´t know.

Does anybody knows if there are ways to prove  that the Netbotz is sending the emails but the problem it´s on  mail server ? 

 

Thanks .

(CID:93914506)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

0 Likes
1
2210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

Hi Luis,

 

Just an added comment to Nathans's answer. Make sure you have added the FQDN for the hostname in the "Network Interfaces" app under Advanced View. I have seen problems sending mail due to this. 

 

Regards,

Breda

(CID:93914522)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

0 Likes
1
2211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

Hi Luis,

Here are a few suggestions for troubleshooting:

  • Check the SMTP server/relay logs to see if it is denying the NetBotz SMTP client for some reason (failed/unsupported authentication attempt like anonymous, unauthorized IP as some mail servers only accept new connections from certain hosts or networks).
    • If the SMTP relay server is running in Microsoft IIS, the log file is beneath the C:\inetpub directory by default.
    • If MS Exchange, you may need to enable the proper diagnostic category before it will appear in Event Viewer. Also, you will need to review the Client Access settings to look for any restrictions by IP/network, SSL/TLS requirements, and supported authentication methods.
  • Run Wireshark/Tshark/tcpdump on the SMTP server to confirm that the connection is being established and not failing due to excessive IP checksum failures or other causes. If you see TCP RSTs from the mail server then it or a firewall (hardware or software) is terminating the connection. A packet capture will also allow you to see the SMTP responses from the server if a connection is successfully established.
  • Investigate to see if any related log files on the NetBotz appliance are accessible. As I recall, there is a log viewer available in the NetBotz web interface if you're on a relatively modern firmware version. I can work to confirm this once I'm in the office tomorrow.

 

(CID:93914508)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

In response to DCIM_Support
0 Likes
0
2211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

Thank you so much !!!

(CID:93915180)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

0 Likes
1
2211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

Hi Luis,

 

Just an added comment to Nathans's answer. Make sure you have added the FQDN for the hostname in the "Network Interfaces" app under Advanced View. I have seen problems sending mail due to this. 

 

Regards,

Breda

(CID:93914522)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

In response to DCIM_Support
0 Likes
0
2211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2024-04-10 12:56 AM

Thank you so much !!

(CID:93915181)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2023-10-31 10:56 PM

0 Likes
0
2211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:18 AM . Last Modified: ‎2023-10-31 10:56 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore