Posted: 2022-01-18 01:58 AM . Last Modified: 2022-01-18 02:03 AM
Does NBWL075 have a POE in a Private LAN port?
Can i connect one CameraPod165 directly to Private LAN port of Netbotz 755 Room Monitor?
In a manual for nb750 stated accurately, that 4 Private Lan Ports have PoE,
but in a nb 755 manual there is no such information aboute Private LAN Port:
.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 07:33 AM . Last Modified: 2022-01-18 08:13 AM
Hi @amyshanov ,
Yes, the private LAN port on the 755 is POE.
Initially I thought the unit (itself powered by POE type2) could power 1 camera, I have since found out that if powered properly, it can power both the docked camera as well as one camera connected to the private LAN.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 08:03 AM . Last Modified: 2022-01-18 08:17 AM
You mean, that to connect two cameras to DCE i must build this desigion:
It seem so strange!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 08:10 AM
Hi @amyshanov ,
I re-verified my previous comment (and will correct it. I am now told that if the 755 is powered properly (POE type 2 @ approximately 36w), it can handle the mounted camera and one on the private LAN without additional power.
DCE is secondary in that config.
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-11 05:17 AM
Could I confirm the rating of the Private Lan ports on Netbotz750 are:
IEEE 802.3at (PoE+) standard, delivering up to 36 Watts ?
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-12 06:03 AM
Hi @amyshanov,
Engineering confirmed that the private ports on the NetBotz 750 and 755 source power via a PoE PSE chip that complies with the IEEE 802.3at standard. The PSE is Type 2 (IEEE 802.3at), capable of up to 30 W per port.