Do we have to do a reset every month on a PDU to get an accurate reading for the kWh.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-15 09:06 AM
Hello @MBender,
DCE reports kWh sensors directly from an SNMP reading from the PDU itself. kWH sensors are a continually increasing sensor until they are manually reset. You may be able to run a report in DCE and look at the Delta Value, which would be the difference between the lowest and highest readings during that time-frame. The lowest should be at the beginning of the time-frame and the highest at the end of the time-frame. This would give you the kWH reading over the course of the selected time-frame only.