Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Dco 8.1 Cooling Plane Type - Calculated Plane

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Dco 8.1 Cooling Plane Type - Calculated Plane
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:37 AM . Last Modified: ‎2024-04-05 04:31 AM

0 Likes
8
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:37 AM . Last Modified: ‎2024-04-05 04:31 AM

Dco 8.1 Cooling Plane Type - Calculated Plane

Hi

i'm having an issue about "Cooling Plane Type - Calculated Plane"

when i press "calculate" i get this issues

  • Vertical Grille Imbalance: Less air is supplied than returned
  • Floor tile airflows did not add up to downflow CRAC airflows

How can i solve it?

Thanks

(CID:126164137)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:37 AM . Last Modified: ‎2024-04-05 04:31 AM

0 Likes
3
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:37 AM . Last Modified: ‎2024-04-05 04:31 AM

HI!

Here is my suggestions:

  1. Check airflow direction in grill properties and airflow values. it should be equal.

      2. When you use vertical grills, you have no needs in CRACS to model airflows.

Now your CRACs and tiles are in different rooms that's why you have second error.

Try to delete CRAC units or "turn off" unit and model it again.

(CID:126164255)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

In response to DCIM_Support
0 Likes
0
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

airflow direction of vertical grille is "out of room"

Crac is underfloor

Tile and Cracs are not in different room

but in this configurarion we have more than 40 rooms

(CID:126164269)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

In response to DCIM_Support
0 Likes
0
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

I dont see CRACS in that room...

You should consider that vertical grills are not works together with CRACs in cooling calculations. So, to model your setup, you need to have grills with "Out of room" direction and the same quantity of "In room" grilles placed under floor. In this case calculations should be correct.

(CID:126164276)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

In response to DCIM_Support
0 Likes
0
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

Sorry

here the cracs

(CID:126164279)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

0 Likes
2
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

Hi Gianluca,

Concerning the Vertical grille imbalance: the total amount of Airflow for "Out of room" must be the same as "Into room", here is to illustrate two vertical grilles, one Out of room, and one Into room, with the same amount of Airflow:

Concerning the floor tiles and downflow CRAC: you have CRAC units placed outside the room, so you might want to enable CRAC's "Duct to ceiling" feature, configure room to use Drop ceiling (if not configured already) and add some ceiling tiles:

Kind regards

(CID:126164437)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

In response to DCIM_Support
0 Likes
0
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

Hi Jef

This is my real configuration

  • Crac Downflow

  • Cold Air inside the room under floor with perdorated tile

  • Hot air outside room by vertical grille

 

 

(CID:126164499)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

In response to DCIM_Support
0 Likes
0
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

Hi Gianluca,

I think the best way to model your configuration could be using Perforated Floor Tile(s) and CRACs (ducted to ceiling) + Perforated Ceiling Tile(s):

You can also add vertical grilles to the model, but make sure that the total airflow (In and Out of room) is in-balance (or just simply not define airflow's, and let them be zero for vertical grilles).

Kind regards

(CID:126164747)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2023-10-22 01:51 AM

0 Likes
0
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2023-10-22 01:51 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore