DCE 7.4.2 Unable to retrieve data from server

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE 7.4.2 Unable to retrieve data from server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

0 Likes
4
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:38 AM . Last Modified: ‎2024-04-05 04:31 AM

DCE 7.4.2 Unable to retrieve data from server

We look after a particular VM DCE server that has been running happily for a few years and had no changes made to it in at least the last few months (since shortly after the 7.4.2 update was released)

Last week (about 9 days ago) and again today, it has come up with the error "Unable to retrieve data from server" on the web browser and I am unable to login using the client at all.  I have managed to download the capture logs from the web interface, but I am not sure how to interpret them. 

 

Please can a Schneider SXW expert assist with this and advise what may be wrong?

The server is quite low resource:-

  • VM Version 10
  • CPU 1vCPU
  • Memory 1024MB
  • Hard Disk 1 18GB
  • Hard Disk 2 60GB
  • Hard disk controller LSI Logic Parallel
  • Network Adapter 1 E1000

Links to the capturelogs files from both incidents are below

2017-10-09

2017-10-16

(CID:126164300)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2024-04-05 04:31 AM

0 Likes
2
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2024-04-05 04:31 AM

Hi Garry,

 

Exactly when did the issue(s) occur? The more accurate you can get with the time/date, the more easily I can find specific time references in the logs.

How did the server again become responsive, did you reboot or simply wait it out?

How many devices are you monitoring and of what type (SNMP, NetBotz, Modbus)?

Are you using surveillance?

If you look at the time this happened, can you check backups, purges, reports, etc to see if something else specific was happening at this time?

 

Looking at the messages log, I can see most of the messages for today look like this:

Oct 16 08:30:03 vlp0722 nbSNMPScan: failScan: Marking scan of 10.36.96.7 with SCAN_FAILED resultcode.
Oct 16 08:30:03 vlp0722 nbSNMPScan: failScan: Marking scan of 10.36.96.9 with SCAN_FAILED resultcode.

Usually failed SNMP scans won't cause the system to lock up but it can't hurt to try to correct any comm issues if you can.

 

Looking at the top output, I can see that the memory is not being overworked:

Mem:   1020020k total,   874388k used,

Swap:  2097148k total,   275756k used,

At least at the time this capture was run, everything appeared to be low enough. Thing is, I'm guessing that since you couldn't get to the web during whatever the issue was, this type of reading could have been drastically different. I'm assuming you got the logs from the web page, correct?

 

the latest NBC.xml appears to be after a reboot with a timestamp of 1507563033882, equating to Monday, October 9, 2017 3:30:33.882 PM


I see a number of errors based on  com.apc.isxc.common.integration.rest.RestExceptionResolver 

Are you using DCO or some other integration? Have you seen any errors there? Anything happen with those systems at the time of the issue?

I also see messages relating to RMS, are you using that as well?

I ask about things like DCO and RMS simply because it's more load on the system. If you say that something happened today (Oct 16) I can't see any specific errors in the log that can account for it. There are at least no exceptions ni java that can account for this issue on that day. There was one on Oct 9 but that shouldn't have an issue on the system today.


Do you use a proxy? I looked at the HTTP error logs that there didn't seem to be much activity between the 9th when the system was rebooted and yesterday. Yesterday and today however, the log is filled with errors:

[Sun Oct 15 22:40:41 2017] [error] (70007)The timeout specified has expired: ajp_ilink_receive() can't receive header
[Sun Oct 15 22:40:41 2017] [error] ajp_read_header: ajp_ilink_receive failed
[Sun Oct 15 22:40:41 2017] [error] (70007)The timeout specified has expired: proxy: read response failed from 127.0.0.1:8009 (localhost)

 

Note that this log starts on Nov 22nd of last year and 1/2 of this log's errors are from just yesterday and today. 

 

When was the last backup or restore performed on this system?


Steve

 

(CID:126164386)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2024-04-05 04:31 AM

In response to DCIM_Support
0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2024-04-05 04:31 AM

Hi Steve - sorry for the delay - the 'private' posts don't seem to send email alerts when they have changed...

 

Not sure exactly when the issue occurred the second time - it was sometime between 1730 on Friday and 08:30 on the Monday.

I did not wait for the server to become responsive as on the first occasion it had been like this for many hours.  The customer shutdown the server using the VM host.  It rebooted again quite quickly.

I have attached a spreadsheet of the device list on the server. 

No cameras.  There are a number of devices offline maybe 10 in total, although the device list does not reflect this - some comms alarms have been disabled.

There are some custom DDF's on the system (written by Schneider) for some non APC cooling units - all identified as RTCS....

No DCO is connected, no RMS.  We use Portal to look at the active alarms on the system though.

No proxy - the DCE server does not have access to the outside world.  We access it via a secured VPN straight to the public interface.

The server was rebooted on the 9th Oct when the issue first was reported (although it may have been in this condition for a couple of days), and again on 16th Oct.

The server has never been backed up - they use some sort of VM snapshot backup system as far as I am aware, although this seems to be on an adhoc basis rather than a regular thing.

 

The last known change on the server was to add 2 more sensors to a Virtual sensor.  I don't recall which sensors they were though...  The changes were made on the 3rd October I think.

The server is currently being updated to 7.4.3 at this very moment.  It has been 'Fixing APC SmartUPS UPS sensors' for over 6 hours now... so much for the 45 minutes claimed when you start the update.  

(CID:126166198)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2024-04-05 04:31 AM

In response to DCIM_Support
0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2024-04-05 04:31 AM

Hi Garry,


As I mentioned, I see tons of HTTP errors on the 15/16 of Oct. but this didn't seem to be the same as what may have happened around the 9th. I guess this could just be another symptom. I don't see anything where I could say do this or stop that to make this issue never occur again. 

I don't know if it's possible but if it does happen again and if you can do a remote session with them, contacting support directly before a reboot could help us get the logs while the issue is happening. That'll not only show us the messages that are happening at that time but also what the resources are saying is being used most and if memory could be an issue.

Increasing memory from 1 gig to 2 or more and increasing processors from a single one (especially if it's shared) could be helpful if it's simply a resource issue.

 

Steve

 

(CID:126166288)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2023-10-22 01:10 AM

0 Likes
0
1270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:39 AM . Last Modified: ‎2023-10-22 01:10 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore