Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO desktop client won't start

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO desktop client won't start
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:45 PM . Last Modified: ‎2024-04-04 12:24 AM

0 Likes
6
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:45 PM . Last Modified: ‎2024-04-04 12:24 AM

DCO desktop client won't start

Hello community,

Our customer can't start their dco desktop client. They enter their username and password and desktop client starts to open with loading bar but client won't open. What could be the problem? Their log files are about 2.7 GB and they can't upload to the box due to security reasons. If you can tell me location of the exact log file you interested, they can send that via e-mail(which must be less than 10 mb or 25 mb). An I ca upload here. This is an emergency situation for our customer so please help me as soon as possible.

Thanks in advance,

(CID:134694119)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:45 PM . Last Modified: ‎2024-04-04 12:24 AM

0 Likes
4
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:45 PM . Last Modified: ‎2024-04-04 12:24 AM

Hi Erhan,

What is the DCO version?

On the server side,

Verify if the DCO server is up and running. It can verified be by going to webmin interface,  StruxureWare DC oOperation > Status page.

What is the spec/OS of client work station?

On the client side,

Is this a new workstation/client? if yes, 

can you/user access the web client for this workstation?

make sure that the client can reach the server - for port requirement please see the following page: StruxureWare Data Center Operation Network Firewall Port Details

make sure the client software installation was okay (or perhaps might have needed admin rights to install)

check if other application/programs (such as antivirus programs) are not blocking the DCO application.

check/test the client connection using port 80 and/or using ssl to connect (443) 

I would basically look into the client application.log file (usually located in Win. C:\Users\\.isxo\DCO version\Operations folder)

Kind regards

(CID:134694239)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

Hi Jef, Thanks for the fast response, The answer are below the questions. In addition, DCO web client stops running last week. Our customer could use DCO before that.

What is the DCO version?

StruxureWare Data Center Operation Server: 8.2.2-74024-c17f64a 

 

On the server side,

Verify if the DCO server is up and running. It can verified be by going to webmin interface,  StruxureWare DC oOperation > Status page.

 Web status - Running

Application status - Running 

Database Status - Running alone

Backup Status - Ok

What is the spec/OS of client work station?

 

On Windows 7

 

On the client side,

Is this a new workstation/client?  NO if yes, 

can you/user access the web client for this workstation?

 

make sure that the client can reach the server - for port requirement please see the following page: StruxureWare Data Center Operation Network Firewall Port Details

make sure the client software installation was okay (or perhaps might have needed admin rights to install)

We have admin rights

check if other application/programs (such as antivirus programs) are not blocking the DCO application.

 

Not blocking, application is marked as trusted

 

check/test the client connection using port 80 and/or using ssl to connect (443) 

 

Using SSL connection

 

I would basically look into the client application.log file (usually located in Win. C:\Users\\.isxo\DCO version\Operations folder)

Application log file is attached

(CID:134694418)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

Hi Jef,

Forgot to add application.log. It is in the attachment.

Best regards,

application.zip

(CID:134694686)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

Hi Erhan,

Thanks - I will take a look and get back to you soon.

Kind regards

(CID:134694695)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2024-04-04 12:24 AM

Hi Erhan,

According to application log, client startup problem seems to be related to work order tasks null pointer exception. I believe similar issue have been resolved in later versions of DCO. Can you/customer test this on a latest release version of DCO (8.2.7).

In general, it is recommended to keep the product updated.

Please let me know if you have questions, or you would like me to test the backup for you? thanks.

Kind regards

(CID:134694754)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2023-10-22 01:44 AM

0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:46 PM . Last Modified: ‎2023-10-22 01:44 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore