Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO can read real time data or just static data only?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO can read real time data or just static data only?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

0 Likes
4
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

DCO can read real time data or just static data only?

cooling.jpg

Hi ,

I got some questions from client during demo. Did DCO's data was static input? because client want to know the real power and CI when using DCO.

DCE can sync real time data to DCO? because client didn't want to use DCO as inventory tools only. they prefer that can read real power data.

 

(CID:153553667)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

0 Likes
2
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

Dear benjamin ip,

The best answer to your customer’s question is from :

We promote DCO as a planning tool & DCE as a monitoring tool. If the client wants to refer to the real time data, DCE is the tool for him. But if he wants to plan something in his data center, such as addition of a server or movement of an asset, then relying barely on the Real time information from the equipment would be insufficient.

To improve this judgement, DCO does Averaging & Peaking of the data for a period at least over 30 days to arrive at the Trend nature of any devices so that maximum information can be obtained from them in order to plan a change.

For example, if you are planning to add a server to a rack & you refer to the present values of the Rack PDUs, without having an insight into the trends of the equipment, you might remain unaware of any Peaks or Sags happened to than Rack in terms of power in the past, which would make the installation vulnerable to such peaks or any similar conditions.

DCO makes the user consider the past data as well for any changes in the environment in order to take care of such vulnerabilities.

In addition, pay attention to the answer of Jef Faridi from post  and the web-link indicated by him:

As described in the following page, the measured peak and average values (in DCO) are based on the the configuration settings (30 days by default):

About Peak and Average Power Data Retrieval from StruxureWare Data Center Expert

Please notice that the displayed measurements in DCO, power peak and average, they are not real-time values but as mentioned they are based on the defined time interval.

This is where you will find information how often the DCO-server polls the DCE-server and more.

I hope this is what you need.

With respect.

(CID:153553676)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

In response to DCIM_Support
0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

Adding to comments from spezialist.

As mentioned StruxureWare DC Operation is designed to be a capacity and planning tool which covers areas like inventory, power path, and capacity planning features. In the power area, the real time data remains at the monitoring level which in most cases would be DCE (data center expert) or ITE (ecostruxure IT expert).

From a capacity planning standpoint, DCO is much more interested in peak and average data from the monitoring system and not the more real time data points. Peaks and averages are important for capacity calculations.

DCO is now transitioning to Ecostruxure IT Advisor so its entirely possible  the exchange between ITA and ITE becomes more seamless than the experience between DCO and DCE today.

Regards

Greg Sterling

(CID:153553993)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

In response to DCIM_Support
0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2024-04-02 11:25 PM

DCO external system.jpg

 

Hi ,

Can DCO connect to DCE by using external system configuration? Cause i want add DCE's KW sensor to DCO layout floor plan. For this purpose, client can know the real time data by external system DCE.

 

Cheers,

Benjamin IP

(CID:153554246)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2023-10-22 01:43 AM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:51 AM . Last Modified: ‎2023-10-22 01:43 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore