Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE offline alert

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE offline alert
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
NF-London
NF-London
Explorer

Posted: ‎2020-08-11 08:06 AM

0 Likes
1
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-11 08:06 AM

DCE offline alert

I have multiple DCE VM's running simultaneously on separate clusters.  Had them for 5 years or more without much trouble.  Recently a cluster has been failing and we have lost a DCE server for a period of time (obviously all the monitoring is lost or not collected for this period too).  The first time it happened I asked the monitoring team to implement a simple ping check to see if the server is still operating.  I was happy at this point. 

 

But barely had I washed the sand out of my toes from holiday and I come back to work learning that the cluster has failed again and the ping test failed because the VM was still responding to a ping even though the service had crashed.

 

My question then is : How can I get an alert to tell me a DCE VM is no longer online or working?   (There is something ironic about my monitoring service not being monitored itself).

 

Here is the guff from the virtualisation team:

Many operating systems will still respond to a ping, even if the service has crashed.  This is a linux feature where is makes the file system read-only, but keep the network stack up to allow you to connect to it.

This is where a service check is required.  Something that test for a running service, or a port that’s only open when the service is running.

A port scan of the o/s might be able to pick up what is open, and that could be requested as a check.

The other alternative is to ask the vendor if there is something that can alert from within the o/s to advise there has been an issue.

 

Thanks in advance

 

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2020-08-11 08:23 AM

0 Likes
0
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-11 08:23 AM

Hi @NF-London ,

 

You could try polling the server using the web API, information on how that works is here:

https://dcimsupport.ecostruxureit.com/hc/en-us/sections/360006467394-DCE-web-services-API

This is merely another way to get data from DCE. Assuming this answers a polling request I still can not say 100% however that this will tell you that all functions of the system are operational. There are multiple processes that must be running for the entire system to be working. Still, it's one of the few ways we can verify data is still being received and available

 

We do have an enhancement request already in the system for what you're asking. Basically a health check of the system. I am adding your post to that request as the more requests that we get on any issue, the more likely it is that engineering and product management will look into adding or fixing any features such as this.

 

Thanks,

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore