can i configure DCE to receive traps from third party devices and show them in alarm window?
BR
Genjua
(CID:134685452)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:01 PM . Last Modified: 2024-04-04 12:40 AM
Dear Genjua,
As far as I know, it is not possible to make DCE as SNMP Trap receiver for third party products.
In order to integrate third party devices and view the alarms, you need to submit a device support request for Device Definition File(DDF) creation if the third party devices support SNMP protocol. Based on DDF request with SNMP Walk file and Management Information Base(MIB) files, you can view the device sensors values and device alarms. It is also possible to create custom thresholds for the third party product sensor values so that you can also view the alarms when the threshold exceeds or value changes.
I hope this helps.
Regards,
Bala
(CID:134685496)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:01 PM . Last Modified: 2024-04-04 12:40 AM
Dear Genjua,
As far as I know, it is not possible to make DCE as SNMP Trap receiver for third party products.
In order to integrate third party devices and view the alarms, you need to submit a device support request for Device Definition File(DDF) creation if the third party devices support SNMP protocol. Based on DDF request with SNMP Walk file and Management Information Base(MIB) files, you can view the device sensors values and device alarms. It is also possible to create custom thresholds for the third party product sensor values so that you can also view the alarms when the threshold exceeds or value changes.
I hope this helps.
Regards,
Bala
(CID:134685496)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:01 PM . Last Modified: 2024-04-04 12:40 AM
Dear Muhammad Genjua,
By the way, once, almost a similar question, has already been asked here at EcoStruxure IT Help. See, for example, threads and .
If you have more questions, please ask.
With respect.
(CID:134685533)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:01 PM . Last Modified: 2023-10-22 01:23 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.