DCE and DCO migration

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE and DCO migration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2023-03-22 05:16 AM

0 Likes
4
1561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 05:16 AM

DCE and DCO migration

Hi team,

 

we have to migrate the virtual machines of a customer from one virtual environment to another. They say that they cannot keep the same IP address in both virtual machines in the new environment. If we change the IP addresses in both virtual machines, are we going to loss all the device associations in DCO?

 

Additionally we have to upgrade the current DCO and DCE to the latest versions of ITA and DCE.  So for DCE, should we have to deploy a new virtual machine in the new environment with DCE 7.9.0 and restore the backup from the old DCE 7.8.x? We will have the license problem because the MAC would change, but we could ask for a new license to our local support. I think it would be better to create new virtual machines in the new environment with the latest versions of DCE and ITA and restore the backups, than migrate the current virtual machines and then upgrade them.  Is this correct?

 

Thanks in advance.

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
gsterling
Captain gsterling Captain
Captain

Posted: ‎2023-03-22 06:32 AM

0 Likes
1
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 06:32 AM

Hello Javier

 

No, changing IP addresses should not cause any problems with your associations. Once ITA and DCE IP's are changed, then in the ITA desktop client, edit the existing entry for the DCE server and change the server IP address if present. If the entry was using the hostname, then as long as the hostname/DNS is updated then things should be fine.

 

If the mac address of the DCE server is changed, then yes your associations will be lost.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

jzurera
Lt. Commander jzurera
Lt. Commander

Posted: ‎2023-03-31 04:40 AM

In response to gsterling
0 Likes
0
1454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-31 04:40 AM

Hi Greg,

 

we have done the upgrade from DCE 7.6.0 to 7.8.1 without problems. After that we have deployed a new DCE 7.9.0 with the same MAC Address that the previous server. Now we have a problem with the restore of the backup from version 7.8.1 to this new server.

 

We have two different backups, one with the configuration and another with the full data, and when we restore some of them in DCE 7.9.0 it seems that works, but when it finishes apparently correctly, DCE 7.9.0 is empty, with the same configuration that it had previously (only the backup location to restore)

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

mayurbhatti
Crewman mayurbhatti
Crewman

Posted: ‎2025-06-10 10:50 AM

0 Likes
1
561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-10 10:50 AM

@jzurera, We are trying to do the same thing. Can you please share some insights and steps that we can follow in order to migrate? Did you manage to migrate all your configuration and data to the new server?

Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
Captain gsterling Captain
Captain

Posted: ‎2025-06-12 03:16 AM

In response to mayurbhatti
0 Likes
0
543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-12 03:16 AM

Hello. I would recommend you use the https://app.ecostruxureit.com/request/ portal to open a general request ticket for DCE so the customer care team can help you with your migration from DCE 7.8.1 to 7.9.0. They will have the details you need to complete the migration.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore