Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE Time Settings off by 1 hour

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE Time Settings off by 1 hour
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

0 Likes
8
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

DCE Time Settings off by 1 hour

DCE Version 7.3.1.114

I've reset the server time on DCE via the System -> Server Administration Settings -> Time Settings ...

tab several times to our ntp server.  After the server reboots, the time reported is correct.  However, after a few days, the time is off by 1 hour, and the check box to "Enable StruxureWare Data Center Expert as NTP server" gets unchecked.

The Server Locale: is set to English (METRIC) and

Server Time Zone:  is set to (GMT-7:00) Mountain Standard Time (America/Edmonton)

 

Any idea why the server time is going off by an hour, and why the "Enable StruxureWare Data Center Expert as NTP server" check box is getting unchecked?

 

Thanks

(CID:140715257)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

Dear Michael Adachi,

Please clarify, is your DCE-server a physical appliance (server) or VMware VM appliance?

If this is a physical appliance (server), you need to make sure that its RTC settings in BIOS are set to GMT.

If this is a VMware VM appliance, then you need to make sure that the checkbox Synchronize guest time with host is not checked:


Hope this helps you.

With respect.

(CID:141269640)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

Hi,

The DCE server is a VM, and the VM appliance is configured as above.

 

Any other ideas?

 

Thanks

(CID:141264813)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:07 AM

Dear Michael Adachi,

Please ensure, that the your external NTP servers are configured to use Coordinated Universal Time (GMT).

Try to check it, for example, with the help of your MS Windows PC and the standard w32tm utility:

textw32tmC:\>w32tm /stripchart /computer:us.pool.ntp.org /dataonly /samples:5 Tracking us.pool.ntp.org [208.87.221.228:123]. Collecting 5 samples. The current time is 19/07/2012 18:36:32. 18:36:32, +03.3575094s 18:36:34, +03.3573679s 18:36:37, +03.3572986s 18:36:39, +03.3570290s 18:36:41, +03.3565357s

Make sure the local time is displayed correctly.

With respect.

(CID:141269643)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:06 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:06 AM

Here is the result of the above command:

C:\>w32tm /stripchart /computer:ntp.yyc.com /dataonly /samples:5

Tracking ntp.yyc.com [10.250.6.30:123].

Collecting 5 samples.

The current time is 2019-03-20 3:05:10 PM.

15:05:10, -00.1674209s

15:05:12, -00.1704247s

15:05:14, -00.1703914s

15:05:16, -00.1704150s

15:05:18, -00.1705623s

(CID:141265251)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:06 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:07 PM . Last Modified: ‎2024-04-03 03:06 AM

Dear Michael Adachi,

Tell us, please, did you solve your problem or not?

With respect.

(CID:141269190)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:08 PM . Last Modified: ‎2024-04-03 03:06 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:08 PM . Last Modified: ‎2024-04-03 03:06 AM

Hi,

The problem has gone away (but I'm not too sure why...)

 

Thank you

(CID:141269614)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:08 PM . Last Modified: ‎2024-04-03 03:06 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:08 PM . Last Modified: ‎2024-04-03 03:06 AM

Ok, very thanks for the good feedback 😀.

(CID:141269639)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:08 PM . Last Modified: ‎2023-10-22 01:21 AM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:08 PM . Last Modified: ‎2023-10-22 01:21 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore