DCE Ports

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE Ports
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

0 Likes
5
2697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

DCE Ports

Hi Team,

               can you please confirm which specific ports need to open for DEC and for APC devices form firewall server, The customer wanted to disable some of the ports on their network and want to ensure the DCE will not be affected.

(CID:105462071)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

1 Like
3
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

Hi Ali,

I think the "FA158328" contains the description for ports used on DCE, here is a copy/paste from the document:

 

The following outlines ports used and their application on any DCE Server:

 

Note: Ports or Protocols preceded by * can be changed from their default port number.

Incoming:

Port 80 (TCP/UDP) - *HTTP Communication from NetBotz Appliances / *ISX Central Console/Web API and 3rd party integrations.

*Port 443 (TCP) - HTTPS Communication from NetBotz Appliances / ISX Central Console

*Port 161(UDP), 162 (TCP/UDP)- SNMP Communication from SNMP Agent

*Port 502 (TCP/UDP)- Modbus TCP Communication from Modbus Device/Gateway Outgoing:

 

Port 80 (TCP/UDP)- *HTTP Communication to NetBotz Appliances / *ISX Central Console / HTTP Post to Web Server/Web API and

3rd party integrations.

*Port 443 (TCP) - HTTPS Communication to NetBotz Appliances / ISX Central Console

*Port 161 (UDP), 162(TCP/UDP) - SNMP Communication to SNMP Agent

*Port 25 (TCP)- SMTP Communication to Email Server

Port 21 (TCP)- FTP Communication to FTP Server

Port 123 (UDP)- NTP Communication to NTP Server

Port 139 (TCP/UDP)- SMB Communication to NAS / SAN

Port 53 (TCP/UDP)- DNS Communication to DNS Server

Port 111 (TCP)- NFS Mount

Port 2049 (UDP)- NFS Communication to NAS / SAN

Port 6000 (TCP)- APC Proprietary Communications protocol for use with AP76xx outlet strips and gen1 PDU on private lan.

Port 445 (TCP)- CIFS Communication to NAS / SAN

Port 502 (TCP/UDP)- Modbus TCP output to Building Management System

*Port 389(TCP/UDP)- Active Directory/LDAP

 

 

Kind regards

(CID:105462081)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

1 Like
3
2696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

Hi Ali,

I think the "FA158328" contains the description for ports used on DCE, here is a copy/paste from the document:

 

The following outlines ports used and their application on any DCE Server:

 

Note: Ports or Protocols preceded by * can be changed from their default port number.

Incoming:

Port 80 (TCP/UDP) - *HTTP Communication from NetBotz Appliances / *ISX Central Console/Web API and 3rd party integrations.

*Port 443 (TCP) - HTTPS Communication from NetBotz Appliances / ISX Central Console

*Port 161(UDP), 162 (TCP/UDP)- SNMP Communication from SNMP Agent

*Port 502 (TCP/UDP)- Modbus TCP Communication from Modbus Device/Gateway Outgoing:

 

Port 80 (TCP/UDP)- *HTTP Communication to NetBotz Appliances / *ISX Central Console / HTTP Post to Web Server/Web API and

3rd party integrations.

*Port 443 (TCP) - HTTPS Communication to NetBotz Appliances / ISX Central Console

*Port 161 (UDP), 162(TCP/UDP) - SNMP Communication to SNMP Agent

*Port 25 (TCP)- SMTP Communication to Email Server

Port 21 (TCP)- FTP Communication to FTP Server

Port 123 (UDP)- NTP Communication to NTP Server

Port 139 (TCP/UDP)- SMB Communication to NAS / SAN

Port 53 (TCP/UDP)- DNS Communication to DNS Server

Port 111 (TCP)- NFS Mount

Port 2049 (UDP)- NFS Communication to NAS / SAN

Port 6000 (TCP)- APC Proprietary Communications protocol for use with AP76xx outlet strips and gen1 PDU on private lan.

Port 445 (TCP)- CIFS Communication to NAS / SAN

Port 502 (TCP/UDP)- Modbus TCP output to Building Management System

*Port 389(TCP/UDP)- Active Directory/LDAP

 

 

Kind regards

(CID:105462081)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

In response to DCIM_Support
0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:16 AM

Thanks jef

(CID:105462098)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:15 AM

In response to DCIM_Support
0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:15 AM

The port information is listed here on our support website on the StruxureWare Data Center Expert Security Webpage: http://dcimsupport.apc.com/display/public/UADCE725/StruxureWare+Data+Center+Expert+Security#Struxure...

(CID:105462110)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:15 AM

In response to DCIM_Support
0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2024-04-09 01:15 AM

Thanks cory

(CID:105462118)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2023-10-31 10:28 PM

0 Likes
0
2695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:01 PM . Last Modified: ‎2023-10-31 10:28 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore