Customer questions

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Customer questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

0 Likes
3
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

Customer questions

I have a customer who has come back with a raft of questions regarding their Netbotz 450. I wonder if someone in Tech support could verify my responses. I apologise in advance if some of these settings are easy to tune from Advanced viewas I am not infront of a unit until I go to this customers site

1) Customer has an MTCBA-G2-U attached to send SMS texts. firmware version is 4.3 as I could not get 4.5 working at the time although in hindsight I may have had other issues masking the problem . Is it safe to advise migrating to 4.5.1. Is it tested with the MTCBA-G2-U or is 4.3 the version I must stick with ?

2) Customer observation. Log retention period varies by sensor (9 hours or 24hours max) but none meet either our desired retention period of a week or our absolute minimum retention of 72hours.

I believe I could add a USB memory stick say 16GB to increase the logging. Is this correct. System would require a re-boot to recognise the external storage. Does external storage have to meet any criteria ie disk storage uSB version ?

3) Customer observation. Logging of hourly temp / humidity is preferable to current 'every change' as it will make the log quicker and clearer for us to check on a daily basis.

What the customer is trying to say is that important messages can either drop off or are masked and wants to see for example 1 degree changes

4) Customer Observation Strange readings on some sensors such as disconnection when server room is inactive (e.g. midnight sunday etc).

Customer mentioned that the temp/humidity sensor and ethernet port has had random entries for disconnection and re-connection. Ethernet I can push to the network team to investigate port settings but I cannot explain sensor behaviour

5)  Customer Observation Smoke detected on the smoke sensor although no smoke in the room.

Again cannot logically explain this as there VESDA system reports nothing. Do units do a self check periodically ?

6) Customer has one leak rope at present. I think I am correct in saying I could extend to 100ft using 5 x 20ft leak ropes. The Netbotz 450 has one leak rope port

 

(CID:105461894)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

0 Likes
1
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

Hi Steve,

 

1: The modem was introduced in an earlier version but newer revisions should not break it. I do not know to what extent this modem was tested with 4.5.1 but I would simply suggest a backup be created just in case.

 

2: You can use USB storage or you can use a remote share. Both will provide retention of much longer periods. There is no specific USB criteria that I am aware of. Please be aware also that if the appliance reboots (which could also happen if using a remote share and connection drops), data may be lost.

 

3: There is no way to change how NetBotz logs. When it sees a change it logs. You can not reconfigure this.

 

4: You should really work with your local tech support on this. We'd need to know the physical configuration, when the sensors experience this condition. If it's always at the same time (at night) what is happening in the environment, etc. Is it always the same sensor? 

More questions depending on config etc. There's simply not enough data to provide an answer to this one. Updating to the most recent may help with this as there have been a number of fixes, some to similar issues. 

 

5: Smoke sensors do not do a self check as far as I am aware. This could be similar to the unplugged error where the system simply senses incorrectly. Again, I would need to know physical config. How many pods, how many smoke sensors ,external power to the pods, etc. This is another one I would also suggest making sure you're up to date on fw.

 

6: Correct, the limit is 100 feet extension. This can be extension using cat5 cables or extension using rope leak extension.

 

Steve

(CID:105461912)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

0 Likes
1
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

Hi Steve,

 

1: The modem was introduced in an earlier version but newer revisions should not break it. I do not know to what extent this modem was tested with 4.5.1 but I would simply suggest a backup be created just in case.

 

2: You can use USB storage or you can use a remote share. Both will provide retention of much longer periods. There is no specific USB criteria that I am aware of. Please be aware also that if the appliance reboots (which could also happen if using a remote share and connection drops), data may be lost.

 

3: There is no way to change how NetBotz logs. When it sees a change it logs. You can not reconfigure this.

 

4: You should really work with your local tech support on this. We'd need to know the physical configuration, when the sensors experience this condition. If it's always at the same time (at night) what is happening in the environment, etc. Is it always the same sensor? 

More questions depending on config etc. There's simply not enough data to provide an answer to this one. Updating to the most recent may help with this as there have been a number of fixes, some to similar issues. 

 

5: Smoke sensors do not do a self check as far as I am aware. This could be similar to the unplugged error where the system simply senses incorrectly. Again, I would need to know physical config. How many pods, how many smoke sensors ,external power to the pods, etc. This is another one I would also suggest making sure you're up to date on fw.

 

6: Correct, the limit is 100 feet extension. This can be extension using cat5 cables or extension using rope leak extension.

 

Steve

(CID:105461912)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

In response to DCIM_Support
0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2024-04-09 01:18 AM

Brilliant thanks for the prompt responses Steve - Top man

(CID:105461916)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2023-10-31 10:22 PM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:54 PM . Last Modified: ‎2023-10-31 10:22 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore