Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Connect Netbotz to Struxureware via Modbus TCP

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Connect Netbotz to Struxureware via Modbus TCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
3
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Connect Netbotz to Struxureware via Modbus TCP

Hello.

I am trying to use a NetBotz rack monitor NBRK0570 as Modbus slave and share temperature and humidity data to a Struxureware AS-P server via Modbus TCP for BMS applications.

I have enabled TCP/IP communication and generated Slave ID for rack and pods.

 

However, when I use a Modbus Scanner for to read the Modbus Map than NetBotz Advanced View gave me, all values I get are 57005 (0xDEAD).

Anyone know why I can´t get the correct values? Should I change another configuration, or something else? Or NetBotz is not useful for Modbus TCP communications if is not used with Data Expert?

 

Thank you!

(CID:149785217)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Hi Gabriel,

 

I've enabled modbus over TCP on my 450. It's similar to the 570 but I didn't have anything connected to it for a quick test:

Then I set up the internal sensor pod as slave 1 and gave the few sensors registers:

Here are my settings using modbuspoll:

I'm getting responses. 0/1 are zero and 2/3 are zero because those are valid values for no smoke and off. 4/5 are 0 (less than 35565 on a 2x 16bit register) and 237 because 74.7 degrees in F is equal to 23.7 C. 

The rest are -8531 (0xDEAD) because that is the output the bot gives if that register is invalid or disabled.

Perhaps you don't have the output enabled?

What version of firmware are you running? I'm at 4.6.4.

The rest is pretty simple, you appear to have the slave and register map configured...I can't speak about the BMS.

 

Steve

 

 

(CID:149785244)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Hi Gabriel,

 

I've enabled modbus over TCP on my 450. It's similar to the 570 but I didn't have anything connected to it for a quick test:

Then I set up the internal sensor pod as slave 1 and gave the few sensors registers:

Here are my settings using modbuspoll:

I'm getting responses. 0/1 are zero and 2/3 are zero because those are valid values for no smoke and off. 4/5 are 0 (less than 35565 on a 2x 16bit register) and 237 because 74.7 degrees in F is equal to 23.7 C. 

The rest are -8531 (0xDEAD) because that is the output the bot gives if that register is invalid or disabled.

Perhaps you don't have the output enabled?

What version of firmware are you running? I'm at 4.6.4.

The rest is pretty simple, you appear to have the slave and register map configured...I can't speak about the BMS.

 

Steve

 

 

(CID:149785244)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2024-04-03 12:22 AM

Hi, 

Try to read holding register 04 then address 31030? The modbus address should be 331030. 

 

Best Regards, 

 

TJ

(CID:149785387)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2023-10-20 05:09 AM

0 Likes
0
1700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:45 PM . Last Modified: ‎2023-10-20 05:09 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore