Connect Leak rope Netbotz 570

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Connect Leak rope Netbotz 570
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

0 Likes
15
2752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

Connect Leak rope Netbotz 570

Hi,

I have a netbotz 570 and I connect the rope leak sensor (nbes0308) to the correct port but I can't see the sensor either in web view neither in advanced view. It's seems like there is no sensor connected to the netbotz appliances. 

The nbes0308 is compatible with the netbotz 570 (view this link)

Sorry if my english was bas, I'm a french speaker.

Edit 1:

It's seems like I have to configure External ports in Advanced view. But I don't know how to fill this form.

 

Thanks in advance.

(CID:108824404)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

0 Likes
0
2752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

NBES0308 should look as per the picture which is shown on our website. 

http://www.apc.com/shop/in/en/products/NetBotz-Leak-Rope-Sensor-20-ft-/P-NBES0308?isCurrentSite=true



The following Inventory should have been there in the NBES0308 box. In case if the adapter is missing, then its cause of the issue. You should use the Rope Sensor Cable adapter for it to be recognized by the appliance. 


I hope this helps. 

Regards,

Bala

(CID:108825704)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

0 Likes
0
2752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

Hi,

If possible, could you please verify once again to see if NBES0308 is connected to the Leak Rope Sensor Port on the 570 Appliance? 

It should detect the sensor on advance view. There is no need to define custom dry contact or analog sensors. The NBES0308 sensor should be detected and shown on advance view after it is connected to the correct port on the appliance. 

 

If it still does not show up as the sensor on advance view, then I would suggest to make sure if the Water Leak Sensor is in good state if you have another working Netbotz 450 or 570 appliance. 

If there is no other appliance available to test, then I would suggest you to try resetting the appliance to factory defaults and try connecting the Water Leak sensor to the Leak Sensor port on the appliance. Please take the backup of the current Netbotz appliance configurations on advance view. 

There are two methods to restore the factory default settings (including user ID and password) on a NetBotz V2/V3 300, 400, 500 series monitoring appliances. Keep in mind that ALL threshold and alert recipients will be reset using this process. 

 Method 1

How to restore the appliance to factory defaults if you know the admin username & password:

WARNING: When restoring the appliance to its factory defaults, only the appliance IP address, subnet mask, and default gateway settings are preserved. All other settings are reset to factory defaults by this procedure.

  1. Open a web browser
  2. Use the following url to reset everything except tcp/ip settings to defaults

http:///unconfig

  1. You will be prompted for an admin username password
  2. After it is entered, you will see a message on the web page that says the following:

Configuration reset requested (keeping basic network settings)....

Reset Initiated

  1. Close the browser
  2. The reset procedure is now complete, you will be able to log into the advanced view or basic (web) view with netbotz/netbotz

 If factory default does not help, then I would suspect the problem may be with either sensor or the appliance port for which you may contact your country service support for further troubleshooting/to obtain replacement if they are under factory warranty. 

I hope it helps. 

Regards,

Bala

(CID:108824430)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

Hi Balaraman Jagadeesan and thank you for your answer.

Yes, the NBES0308 is correctly connected to the Leak Rope Sensor Port on the 570 appliance. 

I don't have another netbotz but I have another leak rope sensor with which I plug it into the netbotz appliance. I have the same results.

 

Before resetting, I wonder if what I had is really a NBES0308 because I don't have Rope Sensor Cable Adapter and Instead of having 4 brooch at the end, I have only 2.

Once again thank you for your help.

(CID:108825693)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

0 Likes
0
2753
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

NBES0308 should look as per the picture which is shown on our website. 

http://www.apc.com/shop/in/en/products/NetBotz-Leak-Rope-Sensor-20-ft-/P-NBES0308?isCurrentSite=true



The following Inventory should have been there in the NBES0308 box. In case if the adapter is missing, then its cause of the issue. You should use the Rope Sensor Cable adapter for it to be recognized by the appliance. 


I hope this helps. 

Regards,

Bala

(CID:108825704)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

0 Likes
10
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

Hi Balaraman Jagadeesan and thank you again for your answer.

 

Finally, I think that I have the APC AP9325 (Not the NBES0308).

I have to do something to detect this sensor in advanced view?

(CID:108826081)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:45 AM . Last Modified: ‎2024-04-08 11:14 PM

The Leak Roper sensor needs to be connected to the Leak Rope Sensor dedicated sensor port on the Netbotz appliance to get it detected on Advance View. I presume that you have got the Rope Sensor Cable Adapter as well as shown in my previous post.

(CID:108826082)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

With the AP9325, we don't need the Rose Sensor Cable Adapter (see this http://www.apcmedia.com/salestools/ASTE-6Z5QA8/ASTE-6Z5QA8_R1_EN.pdf?sdirect=true)

AP9325.PNG

(CID:108826084)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

I have not tested AP9325 with Netbotz 570. Is there any particular reason that you want to try AP9325? As per the Netbotz 570 User Manual, the leak rope sensor part number is NBES0308. I will let the other community members also suggest on AP9325. If it works, then it should be detected by Netbotz 570.

(CID:108826088)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

The AP9325 is the only leak sensor we have (When we order, the dealer suggest us the AP9325). Otherwise, we don't have any particular reason to try the AP9325. The AP9325 will work with other appliances such as...? Thanks.

(CID:108826093)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

As far as I know, AP9325 is used with Close Coupled Air Conditioners such as In-Row Cooling Units. NBES0308 is the correct part number to be used with Netbotz 570 for Water Leak Detection. NBES0308 comes with all the parts such as rope leak sensor, rope sensor cable adapter & CAT-5 cable in order to connect to Netbotz 570's RJ45 connector type Water Leak dedicated sensor port. I also let other community experts to suggest if AP9325 can work with Netbotz 570 appliance as I do not have an experience with it. If AP9325 does not get detected by Netbotz 570 appliance, then I would suggest you to try NBES0308 as its listed as supported sensor part per manual of 570 appliance.

(CID:108826097)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

Ok, thanks. If AP9325 can't work with the netbotz 570, I'll try the NBES0308. I'm waiting for your feedbacks. Thanks again.

(CID:108826106)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

Hi Sylvestre, I am sorry that I am not able to confirm whether AP9325 can be supported by Netbotz or not as I do not have AP9325 with me. If you have AP9325 already with you, please see if you can connect it to the appliance and see if it gets detected by the appliance. If not, you need to use only NBES0308 as described earlier.

(CID:108826163)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

Hi, finally I bought NBES0301 and NBES0308 and all works fine. Thank you for your support.

(CID:110004458)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 AM . Last Modified: ‎2024-04-08 11:14 PM

You are welcome 🙂 Have a nice day!

(CID:110004459)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:47 AM . Last Modified: ‎2024-04-08 11:14 PM

In response to DCIM_Support
0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:47 AM . Last Modified: ‎2024-04-08 11:14 PM

Thanks and have a nice day too 🙂

(CID:110007299)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:47 AM . Last Modified: ‎2023-10-31 10:21 PM

0 Likes
0
2751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:47 AM . Last Modified: ‎2023-10-31 10:21 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore