Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Camera pod 160 lost connection to Netbotz 570

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Camera pod 160 lost connection to Netbotz 570
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

0 Likes
10
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

Camera pod 160 lost connection to Netbotz 570

Hi there!

I have Netbotz 570 and 4 camera pods 160 attached to it. Suddenly one of the pods shows Calibration Template Only in StuctureWare DE and 10 sec loop trying to reconnect in AdvancedView.

I've tried to reboot the appliance and reset all physical connections, but without success. Need some help here. Thank you.

(CID:141272274)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

0 Likes
7
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

Hi Sergei,

What firmware is on the 570?

What is the exact camera model number?

Exactly how are the cameras physically connected to the 570? Are they all directly connected? Any hubs in use? Are they self powered or bus powered hubs? How long are the connections?

Have you tried swapping cables?

Have you tried connecting this camera to where another working camera is connected?

Does this failing camera work if you disconnect other cameras?

Are there any other USB connected pods?

 

Thanks,

Steve

(CID:141272285)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

In response to DCIM_Support
0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

Steve,

 

We have total of 4 of 160 Pods connected on USB to 570 unit, so all ports are occupied.

This one is connected on UNITEK Y-2507 USB 2.0 to RJ45 Extension Converter Cable Active Extension Cable and status shows ONLINE in DCE and it sends out the alerts if I try to disconnect it.

The run is about 50ft.

 

(CID:141272304)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

In response to DCIM_Support
0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

Well, it's not a firmware thing. Again , I'd suggest moving it. Try a regular 16 foot USB cable direct from the 570 to the camera to rule out any cable issues. Disconnect another camera to make sure it's not a power issue. Assuming no other USB pods other than cameras, there would appear to be nothing else drawing USB power. Again, test in a port where a known good camera works.

 

Steve

(CID:141272308)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

In response to DCIM_Support
0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

Just tried to swap USB port with other camera and it appears that the port on 570 is working.

The USB extender cable must be a problem, even though it’s carrying the signal strong enough to show the troubled camera as ONLINE.

 

(CID:141272310)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

In response to DCIM_Support
0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

Steve,

What version of USB port is built in Netbotz 570 and Pod 160? Is it 1.1 or 2.0?

Looking for an USB/Ethernet extender replacement.

Thanks.

(CID:141272632)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

In response to DCIM_Support
0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:47 PM . Last Modified: ‎2024-04-03 02:52 AM

Hi Sergei,

On these units, it's USB 2. What may be the cause is drivers. We don't have drivers for these UNITEK Y-2507 USB 2.0 to RJ45 cables so if they need something specific, that may be what's happening. Most USB hubs and our USB repeater do work.


Steve

(CID:141272658)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2024-04-03 02:52 AM

In response to DCIM_Support
0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2024-04-03 02:52 AM

Steve,

It's is not a new installation and It's been working fine for a couple of years now, but we just started to have an issues with

and ONLINE status.

 

What USB-Ethernet extenders would you recommend or where can I find a list of approved/blessed devices?

Thanks in advance.

 

Sergei.

(CID:141272678)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2024-04-03 02:52 AM

In response to DCIM_Support
0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2024-04-03 02:52 AM

Sergei.

Ok...didn't realize it had been working. If that's the case it likely uses some generic driver. I can't say why it worked and now fails...possibly an issue with the adapter. There is no list of supported extenders as none have been officially tested, we only support regular USB cables, our USB repeater, and most hubs,

 

Steve

(CID:141272687)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2024-04-03 02:52 AM

0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2024-04-03 02:52 AM

There are a number of USB repeater cable on the market that use a complete point of power similar to a USB hub. Since the USB bus provides 5 points of power and the camera pod consumes 4 points of power then it will only leave 1 point of power for the extension. The APC branded USB repeater cable consume .1 for each repeater. So 4 chained together equates to .4. Thus keeping you below 5 points. It is not un common for the camera to work for a while and then fail. This is because there may have been very little activity on that camera. Once data transfer increases with motion then more power is used. Resulting in the camera pod going offline or reporting no image. I would suggest using the APC branded repeater cables. Or injecting a mains power USB hub at the end of the chain.

(CID:143264429)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2023-10-20 05:04 AM

0 Likes
0
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 06:48 PM . Last Modified: ‎2023-10-20 05:04 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore