CRAC units issues

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • CRAC units issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2024-04-03 11:13 PM

0 Likes
2
2383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2024-04-03 11:13 PM

CRAC units issues

Hello

In our new data center we've put new CRAC units, configured and activated.

In the picture below - does it look like normal for you? it seems like the CRAC units don't work at all despite the fact that we configured and activated them.

i'll be happy to hear your opinion/help.

 

 

Thanks.

(CID:137732037)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2024-04-03 11:13 PM

0 Likes
0
2382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2024-04-03 11:13 PM

Can't really see if anything is incorrect from that picture, perhaps you can elaborate more what is the concern?

What I can see form the above picture:

  • CRACs are located on a different room / corridor next to the main DC.
  • There are perforated floors in main DC, showing calculated airflow speed.
  • Depending on the CRAC size, and expected load on racks for that row, it seems the DC has plenty of cooling capacity, as there are some empty rows, presumably for future?

Things to check between actual & modelling, apart from the usual CRAC parameters, perforated floor.

  1. Return of hot air from rack to CRAC, is it ducted? If yes, has all racks and CRACs been configured to be ducted?
  2. Mixed of ducted CRAC and ceiling tiles, see
  3. Non ducted, with wall not reaching ceiling?If yes, the wall between DC and CRAC corridor need to be modeled accordingly.

Try the following, and see if you encounter any error:

  • Look at 3D on calculated plane, see if you have any error about the CRAC configuration
  • Load up racks with servers with heat load, see if CRACs' cooling bar started to increased. 
  • If CRACs cooling capacity is much higher, consider deactivating some to see the changes in CRAC loading when you load some servers to rack in the above step.

 

Lastly some links that I find useful to refer to when configuring cooling:

Tips and tricks for configuring cooling

Designs with CRAC Units Placed Outside the Room

 

If you want to fine tune on the cooling parameter, e.g airflow speed etc, do look into:

Optimizing the Cooling Configuration Accuracy by Adjusting Power and Cooling Estimates

(CID:138809211)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2024-04-03 11:13 PM

0 Likes
0
2383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2024-04-03 11:13 PM

Can't really see if anything is incorrect from that picture, perhaps you can elaborate more what is the concern?

What I can see form the above picture:

  • CRACs are located on a different room / corridor next to the main DC.
  • There are perforated floors in main DC, showing calculated airflow speed.
  • Depending on the CRAC size, and expected load on racks for that row, it seems the DC has plenty of cooling capacity, as there are some empty rows, presumably for future?

Things to check between actual & modelling, apart from the usual CRAC parameters, perforated floor.

  1. Return of hot air from rack to CRAC, is it ducted? If yes, has all racks and CRACs been configured to be ducted?
  2. Mixed of ducted CRAC and ceiling tiles, see
  3. Non ducted, with wall not reaching ceiling?If yes, the wall between DC and CRAC corridor need to be modeled accordingly.

Try the following, and see if you encounter any error:

  • Look at 3D on calculated plane, see if you have any error about the CRAC configuration
  • Load up racks with servers with heat load, see if CRACs' cooling bar started to increased. 
  • If CRACs cooling capacity is much higher, consider deactivating some to see the changes in CRAC loading when you load some servers to rack in the above step.

 

Lastly some links that I find useful to refer to when configuring cooling:

Tips and tricks for configuring cooling

Designs with CRAC Units Placed Outside the Room

 

If you want to fine tune on the cooling parameter, e.g airflow speed etc, do look into:

Optimizing the Cooling Configuration Accuracy by Adjusting Power and Cooling Estimates

(CID:138809211)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2023-10-20 05:03 AM

0 Likes
0
2383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:02 PM . Last Modified: ‎2023-10-20 05:03 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore