BREF2812A

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • BREF2812A
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

0 Likes
16
2045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

BREF2812A

Вопрос: Добрый день. Очередной раз обращаюсь за помощью по чиллеру BREF2812A. Мы с заказчиком перепробовали кучу файлов но так и не нашли нормального файла.

 Было решено привязать чиллер по Modbus но в том что фале, который был на сайте нет всех данных что есть в SNMP-файле. То есть и файл SNMP и Modbus в каждом из них есть то, что нам надо но соединить эти данные ни как. Поэтому прошу предоставить рабочий файл для DCE по протоколу Modbus. Данные, которые мы хотим видеть в приложенном формате PDF. Ах да напомню что данный чиллер не является сторонним продуктом, а принадлежит компании Schneider Electric. Прошу оказывать содействие в наладке данного файла. Готов ответить на все вопросы, если что нужно выслать дополнительно, говорите вышлем.

 https://cloud.mail.ru/public/oWJP/ebzTSwn96

(CID:126166622)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • Cooling Optimize
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 16
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

Мне нужен файл Modbus_DDF по данным из файла PDF по ссылке  https://cloud.mail.ru/public/oWJP/ebzTSwn96

(CID:126169311)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

0 Likes
9
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

Hi amelnikov,

Please tell us the versions of all SNMP and Modbus DDF-files with which you worked, and which do not suit for you chiller BREF2812A.

Further, tell us, please, did you try these two DDF-files, which can be downloaded on request from Device Support:

If not, then try: within one working day for you will be sent links to download DDF-files.

In addition, I highly recommend reading Roman Osadchyi answer in topic . Registration on this resource requires one working day, but it is free.

On the resource you will find a lot of useful information, and in particular, the latest SNMP and Modbus DDF-files, pCOWeb webpages, SNMP MIBs and instructions for Big Chiller - BRE-C-F. So on this resource you can download the following DDF-files:

uniflair_bref_TCPIP_Modbus_chiller - v.5
uniflair_bref_TCPIP_Modbus_chiller_imperial - v.5
uniflair_bref_SNMP_chiller - v.5
uniflair_bref_SNMP_chiller_imperial - v.5
uniflair_bref_SNMP_chiller_multiple - v.5
uniflair_bref_SNMP_chiller_multiple_imperial - v.5

I hope this information will help you in solving the problem. I can not help in more detail unfortunately, since I do not know all the details of the installation of your chiller.

If you have any questions, please ask.

With respect.

(CID:126166717)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:57 AM . Last Modified: ‎2024-04-05 04:19 AM

Hi amelnikov,

Addition to my answer: at the specified link Device Support you can send two absolutely identical SNMP DDF-file:

uniflair_bref_SNMP_chiller - v.2

As you can see from the version of this DDF-file, it is a little outdated. But even it is also recommended to try it.

With respect.

(CID:126167403)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

Modbus

 

Дополнительные OID

 

(CID:126167444)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

Данные фото можно скачать по ссылке

https://cloud.mail.ru/public/4zCu/YEtr1HExh

(CID:126167465)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

По протоколу SNMP и Modbus очень мало значений. Нет нужных значений. В файле PDF ( https://cloud.mail.ru/public/oWJP/ebzTSwn96) есть все нам нужные значения.

Как можно с PDF  транслировать все данные в Modbus?

 

(CID:126167470)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

В данной стать нет решения нашей проблемы. У нас работает связь исправно. Данная статья нам не подходит.

In addition, I highly recommend reading Roman Osadchyi answer in topic PCOWEB - DCE - Uniflair TDAV1622A. Registration on this resource requires one working day, but it is free.

(CID:126167473)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

Научите меня вручную собирать Modbus файлы.

Научите меня вручную собирать SNMP файлы.

Где взять OID = PDF файлу?

(CID:126167474)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:19 AM

Hi amelnikov,

  1. You have not answered my first question about the versions of your DDF-files. Do you know how to look at the versions of DDF-files in the DCE-client? It is important.
  2. You have not answered my second question about the request to download the DDF-file v.2 for your chiller. Did you do it? Have you tried this?
  3. In topic , I wanted to draw your attention to resource http://webcard-it.schneider-electric.com. Is this clear? Did you register on it? Have you been able to download the DDF-files v.5 I have specified for your chiller?

Please, answer fully the above simple questions. And then you will be able to help faster and much better.

With respect.

(CID:126167569)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:18 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:18 AM

http://webcard-it.schneider-electric.com - Да я зарегистрировался на данном ресурсе, скачал все что возможно. Попробовал все файлы подходящие к BREF, безрезультатно. 

На фото, датчики с SNMP v2- Это самый удачный вариант файла. В версии v3 и v5, 50% датчиков могут показывать отрицательные значения. Или вообще писать не подключен.

Я и раньше сталкивался с охлаждением. У меня есть опыт работы Uniflair. Вы смотрите не в ту сторону, я говорю что необходимо сделать нормальный Modbus файл. Так как SNMP перекликается с другими устройствами охлаждения.

 

(CID:126167587)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:18 AM

In response to DCIM_Support
0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:18 AM

Hi amelnikov,

Я и раньше сталкивался с охлаждением. У меня есть опыт работы Uniflair. Вы смотрите не в ту сторону, я говорю что необходимо сделать нормальный Modbus файл. Так как SNMP перекликается с другими устройствами охлаждения.

In order to avoid such problems with SNMP with many devices, it is necessary to fulfill the requirement from file Chillers_DDF.zip\Chillers_DDF\SNMP_WITH_OTHER_CHILLERS_TYPES_OR_CRAC_SERIES\BRE\BRE_pCOWeb_guide.txt where it says:

SNMP PROTOCOL - Multi Family approach

1. Access via FTP (Username = root Password = froot) to the pCOWeb
2. Copy the file snmpoid in this link /usr/local/root/flash/etc/sysconfig
3. Reboot pCOWeb
********************************************************************OR do use the simple procedure as reported in the"Important suggestions area" ===> SNMP OID CHANGE

This is important and if you do this, it will be much easier to correctly discovering of SNMP chillers from a DCE-server.

I hope this helps you.

I was glad to answer your questions.

(CID:126167700)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:18 AM

0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:58 AM . Last Modified: ‎2024-04-05 04:18 AM

Hi amelnikov,

Based on your last question about the problem, I strongly recommend that you create a Device Support Request on page Device Support for your chiller type and specifically for Modbus. Therefore, give there a maximum of information that you consider important with detailed explanations.

I repeat, on the above page, this type of chiller is only supported by SNMP. If you want to discuss or get help on SNMP DDF-files for your chiller, I highly recommend send e-mails to the address specified in the screenshot from resource http://webcard-it.schneider-electric.com:

With respect.

(CID:126167660)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2024-04-05 04:18 AM

0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2024-04-05 04:18 AM

Dear amelnikov,

Have you been able to solve this issue or not?

With respect.

(CID:126171040)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2024-04-05 04:18 AM

0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2024-04-05 04:18 AM

Нет, пока работаем pCOWeb-help@*****

(CID:126171244)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2024-04-05 04:18 AM

0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2024-04-05 04:18 AM

It's great that you asked for help in the right place. I really hope that this will help you.

Thanks again for the feedback 😀.

(CID:126171316)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2023-10-20 05:02 AM

0 Likes
0
2046
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:59 AM . Last Modified: ‎2023-10-20 05:02 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore