Alerts of the DCE when Netbotz is Offline

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Alerts of the DCE when Netbotz is Offline
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

0 Likes
12
2070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

Alerts of the DCE when Netbotz is Offline

Regards,

Dear how could I get StruxureWare alerts when one of the Netbotz is offline?

 

I am using DCE 7.2.6

(CID:97485728)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:36 AM

0 Likes
5
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:36 AM

Francisco,

 

The information I have provided is the answer to your question. There is NO configuration option for what you are seeking under the alarm configuration perspective. That is only for SNMP devices. . The ONLY way to get an e-mail when DCE loses communications with a NetBotz appliance is:

1: Create a user with an e-mail address within DCE

2: Make sure that user has visibility to the NetBotz you need to be e-mailed about (a DCE admin works best)

3: Make sure your e-mail server is configured.

4: Unplug the NetBotz for a test. You may want to select the device menu, NetBotz appliance communications settings, NetBotz appliance polling. hit start for both polling options.

 

You should see that an e-mail similar to the 2 tests I have performed for you. 

Note the subject line:

Critical Communication error with device (device name or IP)

(device name or IP) refers to the NetBotz that has lost comm.

 

the body of the e-mail states:

The device is offline due to a login error.

or depending on the test

The device is offline due to a timeout or connection error.

 

This is the information you receive when the NetBotz loses comm.

 

Steve

(CID:97485805)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

0 Likes
4
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

Hi Francisco,

 

There are, as you've likely seen, no thresholds set in DCE for NetBotz as they are for SNMP devices. This includes lost comm events.  Alerts for lost comm between NetBotz and DCE do get sent however and they are automatic. Any user that is listed in DCE that has both an e-mail address associated with their login (including active directory logins) and has rights to the group where the NetBotz resides should automatically receive the lost comm e-mails.

 

Steve

(CID:97485730)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

Steven,

I want that when a Netbotz lose communication, StruxureWare sent me an alert giving me information that Netbotz is offline. Is that possible?

(CID:117540691)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

Hi Francisco, 

 

You will get an e-,mail similar to the following:

******************************************

From: yourserver@yourdomain.com  
To: youruser@yourmail.com
Date: Tue, Jun 16, 2015, 08:07 AM
Subject: Critical Communication error with device (device name or IP)  
-- Report from yourserver.domain.com_(that server's IP) at
http:/ yourserver.domain.com, at 6/16/15 04:11 PM --

The device is offline due to a login error.
*******************************************************
There is currently no configuration that you can change for this message.
Steve

(CID:117540693)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

Hi Francisco,

 

Although I used a change in login to run yesterday's test, I re-ran it for you today. Please note the conditions do not change. You can not configure what is in the e-mail. You must have a user with an e-mail address that has rights to the NetBotz in question. Here's what you would expect to see in an e-mail where the NetBotz unit lost power.

**************************************************************

From: yourserver@yourdomain.com Show Full Headers
To: youruser@yourmail.com
Date: Wed, Jun 17, 2015, 08:57 AM
Subject: Critical Communication error with device (device name or IP)  
-- Report from yourserver.domain.com_(that server's IP) at
http:/ yourserver.domain.com,, at 6/17/15 08:52 AM --

The device is offline due to a timeout or connection error.

**************************************************************

Please note that the subject line is identical however the body of the e-mail is slightly different. Either issue will cause a no-comm.

 

Steve

(CID:117540705)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:37 AM

Steven I really appreciate your help, I'll explain a little more the case.

As you know, the StruxureWare assumes all thresholds devices that monitors and sends alerts for any of its events, but it is different with the Netbotz as Netbotz manages the shipment of their own alerts.

The StruxureWare not create thresholds for Netbotz, but I need a way for the StruxureWare send me alerts when a Netbotz Device is disconnected from the network.

I am attaching two pictures, in one can see that there is no threshold for Netbotz and the other image I'll show you the default threshold that creates the StruxureWare for a Rack PDU.

 

 

 

 

(CID:117540700)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:36 AM

0 Likes
5
2074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:36 AM

Francisco,

 

The information I have provided is the answer to your question. There is NO configuration option for what you are seeking under the alarm configuration perspective. That is only for SNMP devices. . The ONLY way to get an e-mail when DCE loses communications with a NetBotz appliance is:

1: Create a user with an e-mail address within DCE

2: Make sure that user has visibility to the NetBotz you need to be e-mailed about (a DCE admin works best)

3: Make sure your e-mail server is configured.

4: Unplug the NetBotz for a test. You may want to select the device menu, NetBotz appliance communications settings, NetBotz appliance polling. hit start for both polling options.

 

You should see that an e-mail similar to the 2 tests I have performed for you. 

Note the subject line:

Critical Communication error with device (device name or IP)

(device name or IP) refers to the NetBotz that has lost comm.

 

the body of the e-mail states:

The device is offline due to a login error.

or depending on the test

The device is offline due to a timeout or connection error.

 

This is the information you receive when the NetBotz loses comm.

 

Steve

(CID:97485805)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:36 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:15 PM . Last Modified: β€Ž2024-04-09 04:36 AM

Excellent brother, resolved case!

I followed the steps as you indicated, and the tests were successful.

(CID:97485959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

we had reset our netbotz device, and now many devices in the configuration are reporting 'the device is offline due to a login error'

 

(CID:117540709)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

Hi rtelfer@jennison.com,

It seems to me, that if you want your question answered as quickly as possible, it would be better to create a really new topic, rather than write, in fact an answer, on the theme of two years ago πŸ˜€.

Since you reset the NetBotz appliance settings to their factory defaults, this means also resetting the login and password for access by default (apc/apc). Therefore, either on the DCE-server in the "Add/Edit NetBotz Appliance Credentials" display, you must enter new credentials to access the NetBotz appliance, or in the NetBotz appliance, restore the old login and password.

With best regards.

(CID:117540713)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

Hi rtelfer@jennison.com, I've made a question from you comment here  to get better visibility.

Kind regards,

Stine

(CID:117540728)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

In response to DCIM_Support
0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2024-04-09 04:36 AM

netbotz is not offline, but was physically reset; now can login to struxureware, but many sensors and other devices report 'The device is offline due to a login error'.

 

(CID:117540738)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2023-10-31 10:14 PM

0 Likes
0
2073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 01:16 PM . Last Modified: β€Ž2023-10-31 10:14 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore