APC WATER LEAK - SNMP TRAPS NOT SHOWING FOR WATER LEAK

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • APC WATER LEAK - SNMP TRAPS NOT SHOWING FOR WATER LEAK
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

0 Likes
5
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

APC WATER LEAK - SNMP TRAPS NOT SHOWING FOR WATER LEAK

Need Help , how to detect snmp traps for WATER LEAK DETECTION

(CID:108829111)

Labels
  • Labels:
  • NetBotz
  • Tags:
  • Icon Process Controls
  • iconprocon
  • Leak Detection
  • Leak detection sensor
  • Leak detection switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

0 Likes
3
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

Hi Edwin,

 

Can you please provide more detail? 

What is your physical configuration? NetBotz? Air unit? 3rd party device?

What firmware are you using if it is an APC device?

Are you using StruxureWare DCE and if so, what version?

Have you configured alerts in DCE or on the device itself?

Are you receiving other traps from this leak detection configuration?

 

Any other detail would be helpful.

Thanks

Steve

(CID:108829439)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

In response to DCIM_Support
0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

NETBOTZ 570, using apc water leak rope, snmp traps send to IBM NETCOOL the MIB files we dont have OID for water leak sensor we are receiving other traps for door, temperature

(CID:108829441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

In response to DCIM_Support
0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:11 AM . Last Modified: ‎2024-04-08 04:16 AM

Hi Edwin, What firmware are you running on the 570? Can you try using a simple trap receiver that just shows the network data that is coming in with a trap? If not, can you run a packet capture to verify there is or is not data coming from the appliance when the alert happens? I also don't have netcool to test with so anything I may be able to find will not show up exactly the same as what you may be seeing. I don't have a leak rope that I can test with at the moment but this k-base document shows what type of data you should see if for example it were a spot leak sensor: http://www.apc.com/us/en/faqs/index?page=content&id=FA236815 Until I do (or someone else does) have a chance to test this scenario specifically, have you checked to see if you are getting a trap that doesn't specify the rope leak? For instance, some sensors may not specifically have data specifically listed under enterprises.netBotzAPC.netBotz.netBotzTraps.netBotzSensorTraps and may come across as a generic or "other" trap. I'm assuming you're getting an alert within the NetBotz appliance for this event and that you have the appropriate alert action associated with the sensor and all scheduling is set up correctly. Steve

(CID:108829444)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2024-04-08 04:16 AM

In response to DCIM_Support
0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2024-04-08 04:16 AM

HI Steven, the firmware is 4.5 As IT admin for tivoli. they said they are receiving alerts as below 1. Dewpoint Alarms .1.3.6.1.4.1.5528.100.10.2.3.0.3 netBotzDewPointTooLow DewPoint sensor value too low. .1.3.6.1.4.1.5528.100.10.2.3.0.6 netBotzDewPointUnplugged DewPoint sensor unplugged. .1.3.6.1.4.1.5528.100.10.2.3.0.103 netBotzDewPointTooLowRTN DewPoint sensor value is no longer too low. 2. Temperature Alarms .1.3.6.1.4.1.5528.100.10.2.1.0.2 netBotzTempTooHigh Temperature sensor value too high. .1.3.6.1.4.1.5528.100.10.2.1.0.3 netBotzTempTooLow Temperature sensor value too low. .1.3.6.1.4.1.5528.100.10.2.1.0.6 netBotzTempUnplugged Temperature sensor unplugged. .1.3.6.1.4.1.5528.100.10.2.1.0.102 netBotzTempTooHighRTN Temperature sensor value is no longer too high. .1.3.6.1.4.1.5528.100.10.2.1.0.103 netBotzTempTooLowRTN Temperature sensor value is no longer too low. 3. Humidity Alarms .1.3.6.1.4.1.5528.100.10.2.2.0.3 netBotzHumidityTooLow Humidity sensor value too low. .1.3.6.1.4.1.5528.100.10.2.2.0.6 netBotzHumidityUnplugged Humidity sensor unplugged. .1.3.6.1.4.1.5528.100.10.2.2.0.103 netBotzHumidityTooLowRTN Humidity sensor value is no longer too low. 4. Alarms which are having issues .1.3.6.1.4.1.5528.100.10.2.106 Sensor Unplugged :MIB definition is not having this alarm details .1.3.6.1.4.1.5528.100.10.2.6 netBotzAmpDetectSensorTraps : Alarm is not matching the MIB definition Customer said Please note we are not polling your netboz eMS and are relying on the trap information its sending. The trap is not matching the MIB’s and also find the final below list of alarms which are having issues for now. .1.3.6.1.4.1.5528.100.10.2.10 NnetBotzMicPlugSensorTraps Alarm is not matching the MIB definition .1.3.6.1.4.1.5528.100.10.2.106 Sensor Unplugged MIB definition is not having this alarm details .1.3.6.1.4.1.5528.100.10.2.6 netBotzAmpDetectSensorTraps Alarm is not matching the MIB definition .1.3.6.1.4.1.5528.100.10.2.110 Leak-rope MIB definition is not having this alarm details

(CID:108829493)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2023-10-20 04:57 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:12 AM . Last Modified: ‎2023-10-20 04:57 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore