Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:57 AM . Last Modified: 2024-04-09 12:07 AM
Hi all
If we have a customer that has a CACS and just want his rear door monitored (front door is monitored over a special sliding door at the CACS entry), can he use one AP9361 or NBPD0171 for 2 racks by keeping full functionality as if he has on each rack AP9631/NBPD0171
Regards Christoph
(CID:106204555)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:58 AM . Last Modified: 2024-04-09 12:07 AM
Hi Christoph,
The rack access unit and pod can monitor one or 2 doors on supported racks. It does not matter if you are monitoring a front and rear, 2 front, or 2 rear doors. Please note that the AP9361 has the doors listed as front and rear and this can not be changed but it is simply a label. I'm assuming you're not looking to integrate our handles with any 3rd party system.
Steve
(CID:106204560)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:58 AM . Last Modified: 2023-10-31 10:15 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.