Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Posted: 2020-08-13 05:55 AM . Last Modified: 2023-05-03 12:12 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-13 05:55 AM . Last Modified: 2023-05-03 12:12 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-14 09:20 PM
You should be isolating your SCADA from your control logic.
You should NOT rely upon the SCADA to perform control functionality, it decreases the reliability of the overall system, and complicates diagnostics.
The recommendation would be to push the High High Setpoint into the PLC, and allow it to be changed from SCADA. The PLC will then do the comparison between the PV and the High High SP, and perform the control action based upon this.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.