Working with deciaml numbers in GeoSCADA

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Working with deciaml numbers in GeoSCADA
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-05-25 03:46 AM

0 Likes
11
3075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-25 03:46 AM

Working with deciaml numbers in GeoSCADA

Hi

 

I am working on a project that I need to deal with decimal numbers and also numbers smaller than 1 between 0-1. 

I need to enter setpoint through SCADA and read it by RTU. But regardless of all settings that I have done, any decimal number rounded up or down. I have attached a screenshot of what I need to do. 

 

Any idea how I can access and work with decimal numbers?

I have attached a screen shot of SCADA for your reference. 

 

Thanks

Attachments
Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-05-30 06:20 AM

In response to AndrewScott
0 Likes
0
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-30 06:20 AM

DONE!!!!

Thanks for your patience and kind support.  As you mentioned there was a static variation, but located in a tricky place.

I have changed them to float-precision and also put Control-Object single-precision-float and it worked. 

both sides (RTU & SCADA) are showing correct format of numbers in both output and input. 

 

Thanks again

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
TnTn
Ensign TnTn
Ensign

Posted: ‎2024-05-28 12:04 AM

0 Likes
0
3042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-28 12:04 AM

Have you checked historic list of the point to be sure that the decimal is being stored?

Have you check the format of the point value ?

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-05-28 02:20 AM

0 Likes
1
3051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-28 02:20 AM

The attached screenshot shows you are controlling an analog output point. What Control Object are you using to issue the control? See Configure the DNP3-Specific Control Properties on DNP3 Output Points. If you are using DNP3 g41v1 or g42v2 then the value will be rounded to the nearest 32-bit or 16-bit integer. Obviously, you must use a control object that is supported by the outstation.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-05-28 09:13 PM

In response to AndrewScott
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-28 09:13 PM

Hi Andrew

Thanks for your reply.

Actually these 2 values are DNP3 input analog point, They are 4-20mA analog inputs coming from analyzer to RTU and then scaled. 

I have changed variable to DNP3 analog output and also changed Control Object to  g14v3. but still the same issue.

RTU is Brodersen and correspondent point in RTU is REAL. I couldn't find any float format on RTU side. 

 

I attached screenshot of settings for your reference.

 

Thanks

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-05-29 03:28 AM

0 Likes
1
3014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-29 03:28 AM

I'm a bit confused. The original screenshot shows you are controlling a DNP3 analog output point called "Training.Variable.AO" with a value of 6.7, and the RTU is reporting a value of 7.0 back to Geo SCADA.

 

What DNP3 group/variation is being used by the RTU to report the static value of these points? If it is an integer variation then what scaling (if any) are you applying in Geo SCADA?

Similarly, if the RTU is using DNP3 events to report the value of these points, then what DNP3 group/variation is being used and what scaling (if any) is being applied in Geo SCADA?

 

Based on the "Brodersen Reading.jpg" screenshot I assume this is the RTU applying some scaling and therefore you need to use DNP3 floating point variations for the static data and events reported to Geo SCADA.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-05-29 09:25 PM

In response to AndrewScott
0 Likes
0
2984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-29 09:25 PM

Hi Andrew

 

Sorry for confusion, as I am trying to find a way to do it, I did many changes in both RTU and SCADA sides. But I will stick to 2 main variables that we need in the project. NTU1 and NTU2.

As you can see they are REAL. They are scaled after reading by AI card and then send to DNP3 to forward to SCADA. 

 I have setup DNP3 variables in REAL format and as you can see in SCADA's scaling and formatting tab they have been setup as Number and NOT SCALED. 

 

I have attached screenshots from different settings of both RTU  and SCADA for your reference. 

 Thanks in advance

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-05-30 02:38 AM

0 Likes
1
2970
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-30 02:38 AM

I'm not familiar with Brodersen RTU's but the "DNP3 configuration.png" screenshot shows the static variation and event variation are both "Default". So what are these defaults?

 

https://brodersen.com/dnp3slave/ appears to have information on how these defaults are defined.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-05-30 06:20 AM

In response to AndrewScott
0 Likes
0
2945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-30 06:20 AM

DONE!!!!

Thanks for your patience and kind support.  As you mentioned there was a static variation, but located in a tricky place.

I have changed them to float-precision and also put Control-Object single-precision-float and it worked. 

both sides (RTU & SCADA) are showing correct format of numbers in both output and input. 

 

Thanks again

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

HSullivan
Crewman HSullivan
Crewman

Posted: ‎2024-05-30 04:41 PM

0 Likes
1
2944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-30 04:41 PM

On your configuration page for the RTU, is there an option to change the type from 'analog outputs status' to 'floating point' or something similar? I thinking that it's an issue with how the RTU is sending the DNP values.

 

I am not that familiar with this brand of RTU, but I know with the SCADApacks, the same issue can crop up if the type is set to integer instead of floating point for the DNP3 data type.

Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-06-02 03:38 PM

In response to HSullivan
0 Likes
0
2800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-02 03:38 PM

Hi Sullivan

 

Yes, you are right, the issue was from RTU side. 

As you can see there were a setting that should be done in default variation. It was a little difficult to find. Thanks to @AndrewScott  guide about that.

Regards

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-06-04 01:31 AM

0 Likes
1
2774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-04 01:31 AM

From the above I can see that SCADAPack RTUs are better! 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-06-04 08:50 PM

In response to sbeadle
0 Likes
0
2756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-04 08:50 PM

Yes Steven, I wish we could use SCADA Pack but prices are higher.

Also we have much better support from Schneider. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of