Posted: 2025-04-13 03:32 AM
Hello everyone!
This is my Mimic:
This is my script (called by pick action):
Debug.....
Indeed: "Mimic.Parameters.Target" Object needed
Where am I going wrong?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-22 11:45 PM
The example script states:
Set test = Mimic.Parameters
something = test.Point.CurrentValue
That parameter is now in your variable 'something'.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-14 06:21 AM
Your Pictures are not showing. I would try different file formats or maybe lower resolution.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-15 01:08 AM
I'm so sorry.
I'll try again: my Mimic
My code
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-15 10:18 AM
Interestingly your other picture are now showing.
I believe you need to put the "Mimic.Parameters.Target.FullName" in Quotes.
If it helps here is an example of where I have used FindObject with GetOPCValue. I think GetOPCValue is used so the code can work from a instance of a template.
Function SetPump2AlarmReset()
Dim objCTLcheck
Dim iResponse
Set objCTLcheck = Server.FindObject(Server.GetOPCValue("..IO.Config.Setpoints.Pump 2 Alarm Reset.FullName"))
If objCTLcheck.CheckAccess("CTL") = True Then
Server.SetOPCValue "..IO.Config.Setpoints.Pump 2 Alarm Reset.CurrentValue", 0
Else
iResponse = MsgBox("You do not have Control Privileges to Control " + Server.GetOPCValue("..Name") + "." , vbQuestion + vbOKCancel + vbDefaultButton2, "Station Control")
End If
End Function
I am not sure you are trying to get a database Object information though since I do not see anything in your database tree called Mimic.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-16 01:54 AM
I would like to access the parameters defined for MIMIC as shown in this example
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-22 11:45 PM
The example script states:
Set test = Mimic.Parameters
something = test.Point.CurrentValue
That parameter is now in your variable 'something'.
Link copied. Please paste this link to share this article on your social media post.