Unable refresh outstation

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Unable refresh outstation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
308
AndrewScott
Admiral AndrewScott
97
BevanWeiss
Spock BevanWeiss
91
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
37
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-05-30 04:58 PM

0 Likes
6
1837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-30 04:58 PM

Unable refresh outstation

Hi

 I was reading values from RTU to GeoSCADA. I am trying to refresh outstation to get most recent data from RTU. As you can see in attached file, I try to refresh outstation from object menu, but it is not doing anything.

 

Only when I disconnect and connect RTU to SCADA, it updates outstation data.

 

Any idea why it this happening and how to fix it?

 

Attachments
Labels
  • Labels:
  • DNP3
  • Drivers
  • SCADA
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-06-03 06:47 AM

0 Likes
1
1756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-03 06:47 AM

The comms log shows you've configured a five second scheduled DNP3 integrity poll (this is extremely fast, typically this is hours or days) and you've made around one hundred Refresh requests (which are also DNP3 integrity polls).

The integrity poll responses show that there are six binary input points (g1v1) and two analogue input points (g30v5). The values of these eight points are not changing, except for analogue input 1 which frequently changes by a small amount (less than 0.01).

When the RTU is restarted it is also generating two DNP3 events (for binary input 5 and analogue input 2) which include a timestamp.

 

Which timestamp have you animated on the mimic in the "unable to refresh.jpg" screenshot? I'm guessing it relates to one of the two points that is generating a DNP3 event which is causing it to update. The Refresh should be forcing all eight points to update even though the values aren't changing and I can't see any reason why it wouldn't.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-05-31 02:43 AM

0 Likes
1
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-31 02:43 AM

As your using DNP3 the Refresh method will perform a DNP3 integrity poll. What data is the RTU returning in the response to the integrity poll request and does this include timestamps?

 

You can log the comms between Geo SCADA and the RTU to see what the RTU is doing, see Enable or Disable 'Normal' Communications Logging on a Channel.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-06-02 07:04 PM

In response to AndrewScott
0 Likes
0
1771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-02 07:04 PM

Hi Andrew

 

Regarding data, I have attached screen shot of RTU and data is transmitting to SCADA, They are time-stamped. 

I also attached Pick Action screenshot for your reference. 

I found log file from Server Status but unfortunately I could not translate information in it, to debug what is the issue. 

I have noticed when I stop and run RTU again, data refreshed but while using Pick Action, it is not working. 

Attachments
DriverDNP3 Channel #17761 Comms_001.log
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-06-03 06:47 AM

0 Likes
1
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-03 06:47 AM

The comms log shows you've configured a five second scheduled DNP3 integrity poll (this is extremely fast, typically this is hours or days) and you've made around one hundred Refresh requests (which are also DNP3 integrity polls).

The integrity poll responses show that there are six binary input points (g1v1) and two analogue input points (g30v5). The values of these eight points are not changing, except for analogue input 1 which frequently changes by a small amount (less than 0.01).

When the RTU is restarted it is also generating two DNP3 events (for binary input 5 and analogue input 2) which include a timestamp.

 

Which timestamp have you animated on the mimic in the "unable to refresh.jpg" screenshot? I'm guessing it relates to one of the two points that is generating a DNP3 event which is causing it to update. The Refresh should be forcing all eight points to update even though the values aren't changing and I can't see any reason why it wouldn't.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehdi_Sajjadi
Lieutenant JG Mehdi_Sajjadi
Lieutenant JG

Posted: ‎2024-06-06 03:41 PM

In response to AndrewScott
0 Likes
0
1718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-06 03:41 PM

Hi Andrew

Because of too many changes I re-design and programmed everything from scratch. I lost my track on changes.

1- As you mentioned, I have change polling to 1 hour. 

2- I added a new button to refresh outstation manually by using "REFRESH" action, but no success.

3- timestamp is for outstation.

4- I dig in more in SE help and it seems that this time only updated when we restarting the RTU to check communication health.

5- I added timestamp of one of points ,as you can see it is changing contiguously.

 

If number 4 in above is correct, so we it seems we don't have problem. I need your confirmation about it.

Another question is that if I want to refresh and check connection health, is there any way? as it seems button and adding REFRESH action to it is not working for this case. 

 

Regards

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-06-07 03:31 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-07 03:31 AM

The outstation time property is updated whenever the state of the outstation (healthy, failed, available, disconnected etc.) changes.

The point current time property is updated whenever Geo SCADA receives new data from the outstation for the point. For DNP3 this will either be a timestamp from the RTU or the time that Geo SCADA received the data from the RTU depending on how the outstation and point are configured.

 

If you're using TCP then the outstation state will automatically update if the TCP connection fails.

If you're using UDP or serial then the outstation state will update if the outstation stops replying to requests from Geo SCADA.

If you want to manually check the status of the connection then just perform any action that sends a request to the outstation (refresh, control etc.). If it succeeds (see the event journal) then the connection is healthy.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2024-06-07 02:25 PM . Last Modified: ‎2024-06-07 02:25 PM

0 Likes
0
1702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-07 02:25 PM . Last Modified: ‎2024-06-07 02:25 PM

One device I worked with you could put points in Class 1-3 and not include them in Class 0.

Most devices automatically include point put in Class 1-3 in Class 0, but at this point I would check to see what classes your points are set to and check the documentation on how assigning classes works.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of