Posted: 2025-04-23 09:59 AM
I've set up the new SMS Alarm Redirection following the directions at the link:
https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Tools-amp-Samples/ba-p/279123#toc-hId-129024950...
The documentation (PDF) mentioned being able to set up multiple contact (pager) numbers for a user, which I set up, but I am wondering if there's a way to use the call functionality with multiple users as well? I have tried creating a User Group and attaching different users and then having the method action call the group to no avail.
I'm trying to set this up in a way where there would be a group of "engineers" and maybe "admins" and let's say only the "admins" wanted to receive the call about the alarm notification.
Know anything that might help me out with this? @sbeadle
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-24 02:10 AM
Hi George,
I assume you're using the simple Redirection to SMS: Geo SCADA Expert Simple Voice SMS Redirection via Twilio v6.pdf Also see the demo .sde (Alarm Redirection to Twilio.sde) and interface program (TwilioCallOut program (Feb 2024).zip) below.
I modified the redirection Method Action (User) item to change to a user group:
Then I ensured that each user in the group had a Contact 1 phone number and link to the (dummy) Pager Service in the Contact Information tab.
The redirection Method Action (User) item refers to the logic and passes contact details:
(Check these carefully).
Then, when raising an alarm, the redirection (and therefore the Logic to call Twilio) is triggered separately for each user in that group with valid contacts:
Summary - it works for me!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-24 02:10 AM
Hi George,
I assume you're using the simple Redirection to SMS: Geo SCADA Expert Simple Voice SMS Redirection via Twilio v6.pdf Also see the demo .sde (Alarm Redirection to Twilio.sde) and interface program (TwilioCallOut program (Feb 2024).zip) below.
I modified the redirection Method Action (User) item to change to a user group:
Then I ensured that each user in the group had a Contact 1 phone number and link to the (dummy) Pager Service in the Contact Information tab.
The redirection Method Action (User) item refers to the logic and passes contact details:
(Check these carefully).
Then, when raising an alarm, the redirection (and therefore the Logic to call Twilio) is triggered separately for each user in that group with valid contacts:
Summary - it works for me!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-25 10:52 AM
thanks steve!!!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-03-06 08:54 AM
Wonderful! Thank you for the direction, Steve!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-20 03:10 PM
Hi All,
On the User Rights Assignment, how to create security Setting NTSERVICE/Watchdog_Service, NTSERVICE/autotimesvc....etc? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-10-23 02:36 AM
@MohNasef You need to assign your own Windows user account the "Log on as a service" and "Replace a process level token" privileges. You don't assign these privileges to the other user accounts shown in the screenshot (these are simply other accounts that happened to be on the machine where the screenshot was taken).