Trend Scaling issues in Webx

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Trend Scaling issues in Webx
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
323
AndrewScott
Admiral AndrewScott
118
BevanWeiss
Spock BevanWeiss
100
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxureβ„’ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: β€Ž2020-08-11 07:06 PM . Last Modified: β€Ž2023-05-03 12:12 AM

0 Likes
7
4002
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-11 07:06 PM . Last Modified: β€Ž2023-05-03 12:12 AM

Trend Scaling issues in Webx

Does the IIS based webx in 2017 r3 not support scaling of y-axis?. We are using the IIS based website on 2017 R3 (july 2019) and dont get this option on any type of trends.  Has anyone had this issue before ?

Labels
  • Labels:
  • WebX
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: β€Ž2020-08-11 09:35 PM . Last Modified: β€Ž2020-08-11 09:36 PM

1 Like
6
3991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-11 09:35 PM . Last Modified: β€Ž2020-08-11 09:36 PM

I would probably not invest heavily in the 'IIS WebX' environment.

With GeoSCADA Expert there is a new 'web-based' platform in the form of Virtual ViewX.  From the help documentation (the absence of topics around IIS WebX), it appears that the 'IIS WebX' is largely being left by the way-side.

 

The 'Original WebX' is still where the scripting / XML interaction is based, so it will stay around for a while, but 'IIS WebX' was really just a layer over this, and it never did quite reach the level of maturity that was required of it.

 

Hopefully one of the Schneider people will say that I'm wrong on this, and that your Trends will work beautifully if you tick a box.  But my recommendation would be to revert to the Original WebX in the interim, and investigate whether migrating forward to Virtual ViewX may be the more appropriate solution longer term.

 

Virtual ViewX definitely provides a much better user experience than either the Original WebX or the IIS WebX.  Although it does have some additional administrative considerations.

 

That aside, it does appear that the November 2019 update did have this associated with it:

[SUP-11074] Changed New WebX under IE to use ActiveX to display trends for Trend database objects

 

But you'd have to note that this means you'd need to use IE as the web browser, and retain support for ActiveX controls.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: β€Ž2020-08-11 11:06 PM

In response to BevanWeiss
0 Likes
5
3984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-11 11:06 PM

@BevanWeiss thanks for the reply. 

I Tried exploring the virtual viewx but looking at the hardware requirements I feel it might be very resource intensive. So reverting to original webx might be better and easy in the interim

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: β€Ž2020-08-12 06:27 PM

In response to tkswathik
0 Likes
2
3952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-12 06:27 PM

RemoteApp is built on RDP.  The RemoteApp mechanism is what I would recommend.

They would then launch a full features ViewX client via the RemoteApp.  But since it's RemoteApp, they do not need to have a Windows OS locally.  The ViewX itself is run remotely (on the Microsoft RDS Session Host).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BevanWeiss
Spock BevanWeiss
Spock

Posted: β€Ž2020-08-11 09:35 PM . Last Modified: β€Ž2020-08-11 09:36 PM

1 Like
6
3992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-11 09:35 PM . Last Modified: β€Ž2020-08-11 09:36 PM

I would probably not invest heavily in the 'IIS WebX' environment.

With GeoSCADA Expert there is a new 'web-based' platform in the form of Virtual ViewX.  From the help documentation (the absence of topics around IIS WebX), it appears that the 'IIS WebX' is largely being left by the way-side.

 

The 'Original WebX' is still where the scripting / XML interaction is based, so it will stay around for a while, but 'IIS WebX' was really just a layer over this, and it never did quite reach the level of maturity that was required of it.

 

Hopefully one of the Schneider people will say that I'm wrong on this, and that your Trends will work beautifully if you tick a box.  But my recommendation would be to revert to the Original WebX in the interim, and investigate whether migrating forward to Virtual ViewX may be the more appropriate solution longer term.

 

Virtual ViewX definitely provides a much better user experience than either the Original WebX or the IIS WebX.  Although it does have some additional administrative considerations.

 

That aside, it does appear that the November 2019 update did have this associated with it:

[SUP-11074] Changed New WebX under IE to use ActiveX to display trends for Trend database objects

 

But you'd have to note that this means you'd need to use IE as the web browser, and retain support for ActiveX controls.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: β€Ž2020-08-11 11:06 PM

In response to BevanWeiss
0 Likes
5
3985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-11 11:06 PM

@BevanWeiss thanks for the reply. 

I Tried exploring the virtual viewx but looking at the hardware requirements I feel it might be very resource intensive. So reverting to original webx might be better and easy in the interim

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: β€Ž2020-08-11 11:25 PM

In response to tkswathik
0 Likes
4
3980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-11 11:25 PM

Depending on what the end-user devices are, we've had reasonable success with Microsoft RDP.

I believe there are applications for both Android and iOS devices which provide native support for RDP sessions (and hence likely work well with the RDWeb 'stuff').

If you have more constrained HTML5 only type of devices (like locked down thin-clients), then this wouldn't be an option, but unfortunately neither would the Original WebX (since it requires ActiveX controls).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: β€Ž2020-08-12 07:33 AM

In response to BevanWeiss
0 Likes
3
3963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-12 07:33 AM

By using Microsoft RDP, do users have to remote into some server in your environment and then run IE on it? We are using Microsoft RemoteApp as we have external users needing access to their data hosted in our environment. 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: β€Ž2020-08-12 06:27 PM

In response to tkswathik
0 Likes
2
3953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-12 06:27 PM

RemoteApp is built on RDP.  The RemoteApp mechanism is what I would recommend.

They would then launch a full features ViewX client via the RemoteApp.  But since it's RemoteApp, they do not need to have a Windows OS locally.  The ViewX itself is run remotely (on the Microsoft RDS Session Host).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

tkswathik
Lieutenant JG tkswathik
Lieutenant JG

Posted: β€Ž2020-08-17 02:37 PM

In response to BevanWeiss
0 Likes
1
3899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-17 02:37 PM

Thank you !!

 

I am working on publishing ViewX on RemoteApp, but ran into a different issue it might be better if it is a separate post.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: β€Ž2020-08-17 10:27 PM

In response to tkswathik
0 Likes
0
3892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-17 10:27 PM

Yes please, keeping threads separate for separate issues is very much appreciated.  The search on this forum struggles enough as it is πŸ˜›


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore