Synchronization of Triple Redundant or Triple Redundant with Permanent Standby Systems

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Synchronization of Triple Redundant or Triple Redundant with Permanent Standby Systems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
323
AndrewScott
Admiral AndrewScott
118
BevanWeiss
Spock BevanWeiss
100
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2019-12-03 12:44 PM . Last Modified: ‎2023-05-03 12:20 AM

0 Likes
8
6581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-03 12:44 PM . Last Modified: ‎2023-05-03 12:20 AM

Synchronization of Triple Redundant or Triple Redundant with Permanent Standby Systems

I can't find anywhere in the help files that specifically says it (at least in the way I am saying), but what I suspect, and believe I have observed first hand to be true is that a Standby or Permanent Standby server will only synchronize to the server that is currently Main and listed as a Partner in the Server Configuration. Is that accurate?

 

I'm working with a Triple Redundant with Permanent Standby system. When the Primary server fails, the Permanent Standby server goes offline waiting to connect. The Permanent Standby's Partners don't include the first Standby server that becomes main if the Primary server fails. The Permanent Standby server remains offline until the Primary server becomes main again.

Labels
  • Labels:
  • Redundancy
  • SCADA
  • Tags:
  • redundancy
  • synchronization
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2019-12-03 02:40 PM . Last Modified: ‎2019-12-03 08:17 PM

2 Likes
0
6568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-03 02:40 PM . Last Modified: ‎2019-12-03 08:17 PM

Yes, a server can only sync to a Main and as long as it is configured to see it

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2019-12-03 01:28 PM

0 Likes
0
6573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-03 01:28 PM

Is this looking at the server status itself, or how it appears to ViewX clients?

There is this tick box in the Client Configuration dialog which will prevent connections to 'un-synchronised' servers from ViewX (or other clients using these settings).  This would include any 'standby' servers which are not actively connected to the Main server.

 

If you consider any ClearSCADA architecture, and remove the Main/Duty server, then you don't really have a valid ClearSCADA system.  Since 'Standby' really just means, 'Slave' to the Main (Duty/Active Database)... without a Main there is no valid ClearSCADA system, so nothing for the Standbys to be a slave to.  Them going Offline [or at least exiting the Standby state] (after the expiry of their heartbeat times etc) does make sense.  They should however resume their role as Standby after a Main is brought back up and they have synchronised to it.

Having them still serve 'data' (Config/Data/Historic Data/etc) which may actually not be at all related to the Main Database would typically not be the appropriate thing to do (after all, only the Main server is allowed to create records such as 'Last Known Value' / alarms etc)

 

ClearSCADA Connect to Synchronized Server Only.png

 

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2019-12-03 02:40 PM . Last Modified: ‎2019-12-03 08:17 PM

2 Likes
0
6569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-03 02:40 PM . Last Modified: ‎2019-12-03 08:17 PM

Yes, a server can only sync to a Main and as long as it is configured to see it

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2019-12-03 07:06 PM . Last Modified: ‎2025-08-12 05:13 AM

1 Like
5
6563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-03 07:06 PM . Last Modified: ‎2025-08-12 05:13 AM

There is a tool on Resource Center that may help, link.

Reply

Link copied. Please paste this link to share this article on your social media post.

Hardin4019
Lieutenant Hardin4019
Lieutenant

Posted: ‎2019-12-04 07:35 AM

In response to Anonymous user
0 Likes
4
6550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-04 07:35 AM

Thanks for confirming and sharing the links guys.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-12-05 02:17 AM

In response to Hardin4019
3 Likes
3
6528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-12-05 02:17 AM

1) a Main server can send database sync data to 5 other servers max, 2 standby max and 4 standby-only max. (e.g. total 2 Main/Standby and 4 Standby-only or 3 Main/Standby and 3 Standby-Only)

2) BUT a Standby server can be synced from a max of two servers.

This means that a standby-only can be synced from only two of a triple server set, which is why that link in the post above is needed, which is a tool to "switch parents" of a Standby-Only.

Reply

Link copied. Please paste this link to share this article on your social media post.

MandeepSidhu
Crewman MandeepSidhu Crewman
Crewman

Posted: ‎2022-05-24 04:01 AM

In response to sbeadle
0 Likes
2
3983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-24 04:01 AM

Hi @sbeadle ,

 

PermStdbyServerStateMonitorInstaller.msi

 

Since the move from Resource Centre I can't find this tool anywhere on Community Exchange.

 

I do have a copy from 2018 and I'm sure it'll work as I believe the tool is version independent.

 

Could you please ask someone to upload it to tools together with the documentation?

 

Obviously as this post is migrated, the link from Jesse is taking us to Resource Centre.

 

Thank you

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2022-05-24 04:05 AM . Last Modified: ‎2022-10-19 12:50 AM

In response to MandeepSidhu
0 Likes
1
3979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-24 04:05 AM . Last Modified: ‎2022-10-19 12:50 AM

@MandeepSidhu All of the tools are available from the Geo SCADA knowledge base:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Tools-amp-Samples/ba-p/279123 


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

MandeepSidhu
Crewman MandeepSidhu Crewman
Crewman

Posted: ‎2022-05-24 04:17 AM

In response to AndrewScott
0 Likes
0
3975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-24 04:17 AM

@AndrewScott Thank You!

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore