Switched to a Shared Outstation Set - Nuisance Comm Alarm from Spotty Backup Channel

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Switched to a Shared Outstation Set - Nuisance Comm Alarm from Spotty Backup Channel
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
95
BevanWeiss
Spock BevanWeiss
89
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Tanquen
Lt. Commander Tanquen
Lt. Commander

Posted: ‎2021-09-16 12:09 PM . Last Modified: ‎2023-05-03 12:01 AM

0 Likes
2
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-16 12:09 PM . Last Modified: ‎2023-05-03 12:01 AM

Switched to a Shared Outstation Set - Nuisance Comm Alarm from Spotty Backup Channel

They have around 30 sites that use radio and Modbus to talk to SCADAPacks at each site.

 

They have a newly added Cell Modem at one site so we setup a New Shared Outstation Set added the Serial and TCP channels to it and converted all the sites Outstations to shared Outstations to use the new Shared Outstation Set and it in turn uses the Serial channel for Line A and the TCP channel for Line B. All the sites with only a radio, have their switch type set to Fixed on Line A. Only the one site with a Cell Modem and Radio is set to Independent with Line B (the Cell Modem) as the Preferred Line.

 

This all seems to work on the two servers but some of the view nodes show random communication errors at some of the sites. The two servers do not, they show all sites communicating. Maybe the view only nodes did not sync everything but they are not polling so it's odd.

 

The main issue now is the one site with Cell and Radio keeps showing a comm loss error on the Radio Channel. That is why this site has the Cell Modem as the Radio is spotty but can get data. Is there a way to lessen the nuisance Comm Fails for this site?

 

It's Preferred Line B to the Cell is ok but it would be nice not to get the Line A channels comm fail alarm every five minutes or so.

 

We enabled the Heartbeat on the sites Shared Outstation so that if it fails over the the Radio it will move back to the Cell Modem when it is back up. If we don't it looks like it will stay on the Radio as it gets data often enough not to cause a failover. This also seems to stop the Line A channels comm fail alarm but then it will not fail back over from then Radio when the Cell Modem comes back.

Labels
  • Labels:
  • Drivers
  • Radio
  • RTU
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-09-16 08:45 PM

0 Likes
0
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-16 08:45 PM

So you have a central 'office' which has two Geo SCADA Expert servers, and a number of ViewX clients ('view only nodes')?

 

ViewX can only get it's data from a server.  So if the server is showing healthy communications, then all the clients shall be showing healthy communications for those sites also.

If you're seeing otherwise on the ViewX clients, then it might pay to confirm that the ViewX clients are pointing at the servers that you believe they are.

 

The outstation that has the two channels available should be showing 'Healthy, Multidrop' if both channels are available (according to heartbeats) and will change to 'Healthy, A Failed' or 'Healthy, B Failed' depending on which channel fails of the two.

If we expect noisy failures, we will often disable alarms from the outstation entirely.

And then implement alarming via some logic, and an internal digital alarm point, this lets us have more control over what is a failure, and how long before the failure is alarmed etc etc.

It can also be possible to do the time masking stuff by using Alarm Severities which are not displayed, and then alarm redirections to escalate the Severity into a displayable range.  But that does have quite a bit of reconfiguration and maintenance overhead to it.  Especially if you've started with the default 1 (Low) through 1000 (Critical) alarm severities... really doesn't leave you any obvious gap at the bottom to put hidden alarms. 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Tanquen
Lt. Commander Tanquen
Lt. Commander

Posted: ‎2021-09-20 09:03 AM . Last Modified: ‎2021-09-20 09:08 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-20 09:03 AM . Last Modified: ‎2021-09-20 09:08 AM

There are only the two servers. The view node with the issue is on a laptop so maybe it's not fully synced or did not update correctly. All the other view nodes also look at the same servers and are ok as was the laptop top before the Outstation reconfig. Everything should be coming from the servers so it seems odd that one view node thinks there are different communication errors. Maybe the operator is misstaken or it's a 2020 bug like the online help just opening a black screen?

 

For the Nuisance Comm Alarms we just disabled the Heartbeat. So it should fail over to the radio if the cell modem goes out but won't fail back to the preferred line unless the radio fails completely but it gets rid of the random communication alarms. It's always spotty but not enough to fail back over to the cell modem.

 

We just added a button to use the switch line function so the operators can put it back.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of