Stop sequential polling of SNMP points if SNMP device is marked as 'Failed'

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Stop sequential polling of SNMP points if SNMP device is marked as 'Failed'
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
308
AndrewScott
Admiral AndrewScott
98
BevanWeiss
Spock BevanWeiss
91
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
37
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
rlao
Lt. Commander rlao
Lt. Commander

Posted: ‎2021-06-03 10:05 PM . Last Modified: ‎2023-05-03 12:03 AM

0 Likes
4
1642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-03 10:05 PM . Last Modified: ‎2023-05-03 12:03 AM

Stop sequential polling of SNMP points if SNMP device is marked as 'Failed'

Hi,

 

Due to the single-threaded nature of the SNMP driver, we have backlog issues on our SCADA system when several of our SNMP devices goes offline, because the driver is stuck waiting on timeouts for each individual SNMP point for those offline devices. This is a problem when we have quite a lot of SNMP devices out there on our network.

 

To address this, we have a logic script that disables all SNMP points of a failed device except for one until that one single SNMP point comes back online, after which the script will re-enable all the other SNMP points for that device.

 

Is there a way we can achieve something more elegant in the SNMP device settings? Like if the SNMP device is found to be bad, then stop polling all its assigned points until the device health improves again. Or does the SNMP device health in GeoSCADA directly depend on whether those SNMP points are online?

Labels
  • Labels:
  • Drivers
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-06-07 04:07 PM

0 Likes
3
1620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-07 04:07 PM

I think this is unfortunately just the way the current SNMP driver (and largely SNMP) is..

 

An SNMP Device (in GeoSCADA) itself is really only a placeholder for an IP address and a base OID.

It doesn't do anything on its own.  You need to have a point associated with it before it starts to do anything.  And I've found that it doesn't do anything 'smart' with collections of points, they still all seem to get treated separately, without any optimisation performed as to their scanning (I can't recall what ability there is in SNMP for this.. I'm pretty sure there is like a 'bulk get'.. which from memory GeoSCADA never uses).

 

My solution has been to always try to avoid SNMP for anything operationally critical.

I only really use it for monitoring a few UPS status signals (i.e. last test, last test battery life expectancy etc).. critical signals like 'On Battery' I still prefer to get via Modbus / DNP3 to an adjacent controller.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-06-07 04:07 PM

0 Likes
3
1621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-07 04:07 PM

I think this is unfortunately just the way the current SNMP driver (and largely SNMP) is..

 

An SNMP Device (in GeoSCADA) itself is really only a placeholder for an IP address and a base OID.

It doesn't do anything on its own.  You need to have a point associated with it before it starts to do anything.  And I've found that it doesn't do anything 'smart' with collections of points, they still all seem to get treated separately, without any optimisation performed as to their scanning (I can't recall what ability there is in SNMP for this.. I'm pretty sure there is like a 'bulk get'.. which from memory GeoSCADA never uses).

 

My solution has been to always try to avoid SNMP for anything operationally critical.

I only really use it for monitoring a few UPS status signals (i.e. last test, last test battery life expectancy etc).. critical signals like 'On Battery' I still prefer to get via Modbus / DNP3 to an adjacent controller.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

rlao
Lt. Commander rlao
Lt. Commander

Posted: ‎2021-06-15 10:35 PM

In response to BevanWeiss
0 Likes
2
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-15 10:35 PM

Hi Bevan,

 

Yes, it seems like the concept of an SNMP device in ClearSCADA is superficial and only serves to improve configuration efficiency, rather than influence the scanning behaviour of the driver. There doesn't seem to be any configuration on the SNMP device/points that I can do to make the scanning 'smarter'.

 

I've since opened up a ticket to discuss this directly with support, but thanks for reaffirming what I suspected.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-06-16 03:25 PM

In response to rlao
0 Likes
1
1586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-16 03:25 PM

It might end up a little bit 'political' in regards to SNMP improvements.

 

In the radio space, there are predominantly two competing 'brands'.

Trio, and 4RF.

 

Trio are a Schneider product, and use Trio Diagnostics (Trio Advanced Diagnostics is the improved driver for it).

4RF use the more industry supported SNMP..

 

Hence, for Schneider to maintain strong market share in the radio space with Trio, there is incentive for them to NOT have a particularly good SNMP driver.  If there was a better SNMP driver in GeoSCADA, quite a lot of telemetry customers would migrate from Trio radios to 4RF.

 

I have been asking for an 'Advanced' SNMP driver for over 5 years... unfortunately there have been very few improvements at all to the SNMP driver during that time (whilst the Trio Diagnostics protocol received an entirely new development in the 'Advanced' driver range).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-06-27 04:03 PM

In response to BevanWeiss
0 Likes
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 04:03 PM

Every SNMP device should expose the uptime (.1.3.6.1.2.1.1.3.0) so it is not outside the realms of feasibility that if you use the device model (rather than the old way of configuring each point with the host/community/etc details) that when the device "polls" it first does a poll to the uptime and see if that returns valid data before worrying about any attached point. Would probably have to be enabled/disabled by some tickbox though in case something doesn't expose uptime (e.g. restricted by ACLs)

 

Could be worth adding something to the suggestion forum requesting something like this.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of