Settings for a User to View Only a Specific Page

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Settings for a User to View Only a Specific Page
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
315
AndrewScott
Admiral AndrewScott
105
BevanWeiss
Spock BevanWeiss
95
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
abdullah123456789
Lt. Commander abdullah123456789
Lt. Commander

Posted: ‎2024-01-25 11:12 PM . Last Modified: ‎2024-01-28 10:24 PM

0 Likes
3
966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-25 11:12 PM . Last Modified: ‎2024-01-28 10:24 PM

Settings for a User to View Only a Specific Page

Hello,

 

I am using Geo SCADA Expert 2021 February 2022 version. I need to create a user and this user should view only specific page and shouldn't view any different page. Also this user should not be able to take any action. Which of the default settings should I change when I create a new user? 

Labels
  • Labels:
  • SCADA
  • ViewX
  • WebX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-01-29 05:53 PM

0 Likes
0
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 05:53 PM

You should probably create a user group object with only the read (not browse) permission on the mimic object (and any embedded mimics object), create your new user object and only add them to that user group, and then set that user's homepage to the mimic you want them to see & tick the box saying show home page at login (under the ViewX tab).

 

The res of the settings on the user object itself are really up to you, most you probably wont want to have ticked but it really comes down to your actual requirements (such as should they see the alarm banner, if so should they hear alarms, etc). Probably the best way is start by disable everything for that user and see, and tweak upwards.

 

There are also some client-side settings in File -> Options that may impact the experience for the user you should check out.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
tfranklin
Commander tfranklin
Commander

Posted: ‎2024-01-29 06:28 AM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 06:28 AM

The easiest thing here would be to create the user and just not associate him with any user groups.  On the screen he needs, give him read access. 

 

This becomes more of a complex issue though depending on what data you need visible on the screen.  The user needs read access to any/all objects that will be visible on this display.  With that in mind, it may be best to associate him with a user group or manually define him on the group(s) he needs to see. 

 

If there's not a ton of things he needs access to, you could always duplicate some of the tags or use calculation tags or something to derive the values and house them in his own personal folder where it's the only thing he can access. 

Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodlandToo
Lt. Commander AdamWoodlandToo
Lt. Commander

Posted: ‎2024-01-29 05:53 PM

0 Likes
0
955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 05:53 PM

You should probably create a user group object with only the read (not browse) permission on the mimic object (and any embedded mimics object), create your new user object and only add them to that user group, and then set that user's homepage to the mimic you want them to see & tick the box saying show home page at login (under the ViewX tab).

 

The res of the settings on the user object itself are really up to you, most you probably wont want to have ticked but it really comes down to your actual requirements (such as should they see the alarm banner, if so should they hear alarms, etc). Probably the best way is start by disable everything for that user and see, and tweak upwards.

 

There are also some client-side settings in File -> Options that may impact the experience for the user you should check out.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-01-30 02:22 AM

0 Likes
0
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-30 02:22 AM

I really wanted to mark both answers as solutions!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of