Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Sensitive menu with Hover function

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Sensitive menu with Hover function
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Zartur10234
Zartur10234
Explorer

Posted: ‎2025-07-04 03:24 AM . Last Modified: ‎2025-09-04 02:09 AM

0 Likes
7
1460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-04 03:24 AM . Last Modified: ‎2025-09-04 02:09 AM

Sensitive menu with Hover function

Hello,

I'm trying to create a dropdown menu that appears when you hover over it. The issue I'm facing is related to PosVal: when I hover over it, it starts looping between the new position and the old one.

I tried using a different item, resizing it with the size parameters, and creating a group with the menu options, but it didn't work as expected.

 

Zartur10234_0-1751624572065.png

(Example of what I'm trying to create)

 

Any suggestions?

Labels
  • Labels:
  • Mimics
  • ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
sbeadle
sbeadle Champion
Champion

Posted: ‎2025-07-31 08:03 AM

0 Likes
0
1394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-31 08:03 AM

We probably need more specifics.

Assuming you don't want to use the menu. features in script, can you control the visibility of the menu?

Not sure why you'd use PosVal, unless you need to move it up and down?

Reply

Link copied. Please paste this link to share this article on your social media post.

periksson
periksson
Explorer

Posted: ‎2025-08-01 03:22 PM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-01 03:22 PM

This might be a way to have the effect you desire:

1. Have a button (or text) with a rectangle that blends in with the background:

periksson_0-1754086729228.png

2. Group the objects together, set "Visible" to False and Hover:

periksson_1-1754086817064.png

3. Have your buttons built out for the menu:

periksson_2-1754086869845.png

4. Place those buttons behind the group. Now when you hover, it will hide and expose the menu underneath.

The only caveat is that this applies to the empty space taken up by the rectangle used to "hide" the entries. When you hover over that empty space, it will reveal the list. That's the only way I could think of to generate the visual.

 

I personally prefer the built-in Form builder, even at the cost of an extra click to initiate the menu.

Reply

Link copied. Please paste this link to share this article on your social media post.

Zartur10234
Zartur10234
Explorer

Posted: ‎2025-08-03 11:31 PM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-03 11:31 PM

To answer both:

I want to manage the visibility of the menu by hovering over the button, not by clicking it. Moving the buttons would be a way to hide the other options so that they appear only when I hover over the main button.

 

The issue with the proposed solution is that once you hover over the entire block—not just the menu button—everything appears. Also, it would only work if there weren't any borders or background colors interfering.

 

Btn1.pngBtn2.png

 

Also, I just noticed a weird resolution issue while zooming in and out. Sometimes you can see the borders of the item underneath the box.

 

Btn3.png

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2025-08-05 01:38 AM

0 Likes
1
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-05 01:38 AM

Can't see those images are they jpg or png? Not sure why they are not visible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Zartur10234
Zartur10234
Explorer

Posted: ‎2025-08-06 11:08 PM

In response to sbeadle
0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-06 11:08 PM

the images are .png, i will reupload them as jpg in the same order as the previous post

Btn1.jpgBtn2.jpg

Btn3.jpg

   

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2025-08-28 03:43 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-28 03:43 AM

Perhaps if you still need some advice you could add an example .sde file into this thread?

 

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
sbeadle Champion
Champion

Posted: ‎2025-09-04 02:09 AM

0 Likes
0
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-04 02:09 AM

Thread is dormant, marking as informational.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore