Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
307
AndrewScott
Admiral AndrewScott
96
BevanWeiss
Spock BevanWeiss
90
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
36
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
Oncom
Commander Oncom
Commander

Posted: ‎2020-01-21 12:58 AM . Last Modified: ‎2023-05-03 12:18 AM

0 Likes
9
6683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-21 12:58 AM . Last Modified: ‎2023-05-03 12:18 AM

Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server

 

ArchitectureArchitecture

Hi All,

 

I have architecture above. 

- 2 Server, 1 server in control network, and 1 server in office network. and both are connected directly peer to peer. 

- 2 separate network.

 

is it architecture is possible?
I was trying to configure as redundant, but it become a problem when Server B as MAIN

what I want is Server A always as MAIN / Primary. and Server B can synchronize data from Server A and Server B can accessed by Client B.

 

thanks
 😀

www.pamtek.co.id
Labels
  • Labels:
  • Redundancy
  • SCADA
  • Telemetry
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-01-22 12:46 AM

In response to Oncom
2 Likes
5
6648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-22 12:46 AM

You might want to raise this with support, we can help you more effectively in through the correct channels.

 

If you right click the server icon and select Invalid Configuration it will tell you why your configuration is invalid.

 

Use a name or address that doesn't exist at all, rather than one that just doesn't have CS installed. We use ICMP as one component for detecting isolation, it doesn't rely on CS replying. I recommend using 'Dummy' or similar, so someone else who looks at the config in future doesn't think it is a mistake.

 

See below what I think will work for you. I'm not 100% sure what each machine's IP address is, I've assumed:

 

Main (A) is 129.76.3.1

Standby (B) is 129.76.3.3

 

Dummy should be configured for the Main's Standby A and the Dummy's Standby B.MainPartner.JPGStandby.JPGMainPSs.JPG

 

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-01-21 01:02 AM

1 Like
8
6678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-21 01:02 AM

Yes, configure server B as a Permanent-Standby. It will serve data and sync from A, but never go Main.

See this new video for architecture guidance:

https://www.youtube.com/watch?v=lmbMy4jJGX0&list=PLa7UGrWOTyjnPpCJxnTZkdBM_6D70qoKl

Search for Permanent Standby in the F1 help.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-01-21 08:02 PM . Last Modified: ‎2020-01-21 08:05 PM

In response to sbeadle
1 Like
7
6660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-21 08:02 PM . Last Modified: ‎2020-01-21 08:05 PM

To have B as a permanent standby you'll have to either install an additional hot standby on the control network side (recommended) or configure the permanent standby so it thinks there are is an additional hot standby - the permanent standby needs to have two hot standby partners configured.


NoName.JPGDummyName.JPG

Reply

Link copied. Please paste this link to share this article on your social media post.

Oncom
Commander Oncom
Commander

Posted: ‎2020-01-22 12:08 AM . Last Modified: ‎2020-01-22 12:09 AM

In response to Anonymous user
0 Likes
6
6653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-22 12:08 AM . Last Modified: ‎2020-01-22 12:09 AM

@sbeadle Hi Steve, thanks for your respond.

in your video, and also mentioned by @Anonymous user the MAIN server should have standby pair. so is it still possible?

image.png

 

 


I was try to configure it but fail. my Permanent standby Server doesn't start: always in state: Starting.. 

I configure Permanent Standby Server as on Manual Help 

SC_OPCSERVER(STANDBY).PNG

 

and here is my configuration on MAIN server:

SC_SCADASERVER(MAIN)_PERMANENT.PNGSC_SCADASERVER(MAIN)_STANDBYTAB.PNG

 

what I was trying in MAIN Server:
-put IP adress of StandbyPC(permanent standby) on Standby A : Permanent standby PC can start but show up Error Invalid configuration, Main Server also show invalid configuration

 

-put IP address of Main PC (this computer IP it self) : Main Server can start as Main, Standby Server always in Starting state

 

-put IP address of other PC (no clearscada) : Main Server can start as Main, Standby Server always in Starting state

www.pamtek.co.id
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-01-22 12:46 AM

In response to Oncom
2 Likes
5
6649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-22 12:46 AM

You might want to raise this with support, we can help you more effectively in through the correct channels.

 

If you right click the server icon and select Invalid Configuration it will tell you why your configuration is invalid.

 

Use a name or address that doesn't exist at all, rather than one that just doesn't have CS installed. We use ICMP as one component for detecting isolation, it doesn't rely on CS replying. I recommend using 'Dummy' or similar, so someone else who looks at the config in future doesn't think it is a mistake.

 

See below what I think will work for you. I'm not 100% sure what each machine's IP address is, I've assumed:

 

Main (A) is 129.76.3.1

Standby (B) is 129.76.3.3

 

Dummy should be configured for the Main's Standby A and the Dummy's Standby B.MainPartner.JPGStandby.JPGMainPSs.JPG

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Oncom
Commander Oncom
Commander

Posted: ‎2020-01-26 10:16 PM

In response to Anonymous user
0 Likes
3
6591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-26 10:16 PM

@Anonymous user Hi,

 

I was try again using that configuration from you. but still the Standby doesn't want to Start, the state always: Starting..

already change the port too in permanent standby tab to 5482, and still didn't work

 

BTW, to raise this with support, do we need to have support/CF? or just simply email to Trss-support@se.com or your email 😉?

 

 

Thanks

www.pamtek.co.id
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-01-26 10:30 PM

In response to Oncom
0 Likes
2
6588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-26 10:30 PM

When you ping the Primary Server IP address from the Permanent Standby server what result do you get?

If that doesn't work, then you need to fix that issue.

 

If that does work, then you should try TCPing (or telnet) to the default port 5481 to ensure that this works.  If it doesn't, then you likely have a firewall problem.

 

The IP addresses that you have listed seem a little unusual based upon the first image that you have suggested.

I would have expected that you would be using link local addresses for the direct link between the two servers (Primary and Permanent Standby), and hence would have 169.254.x.y format IP addresses.  You could allocate a Class A, B or C private IP address (or even technically a public IP address) to these interfaces, but it seems wasteful if they will only be used to link these two computers together for the ClearSCADA data replication.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Oncom
Commander Oncom
Commander

Posted: ‎2020-01-26 11:05 PM

In response to BevanWeiss
0 Likes
1
6585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-26 11:05 PM

hi @BevanWeiss ,

 

I can ping from each others, and firewall has been disabled on both side. I already successful configure it as Redundant pairs. that 5481 port should be OK then.

 

Yes this is unusual Class B IP address using public IP, I already mentioned it to them (my customer) to use private IP as a standard.

and the link between computers is only connected each others for data replication.

www.pamtek.co.id
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-01-26 11:21 PM

In response to Oncom
0 Likes
0
6582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-26 11:21 PM

I would recommend leaving all ports as default 5481.

 

If you have already successfully configured the servers as redundant pairing, then you should just need to go to the Permanent Standby, and change the mode on this server (the Permanent Standby) from Hot-Standby Pair, to Permanent Standby, and things should work.  If it complains about wanting a Standby B address just enter 0.0.0.0 for this.

 

You will absolutely need to have the Primary Server running first, for the Permanent Standby to transition from Starting to Synchronising. And then once Synchronised it should just run as Permanent Standby from that point until the Primary Server is lost, in which case it will revert to Starting (until Re-synchronisation can occur again).

 

To get official tech support, you would need to have a Site ID that is in support (technically all sites that you are involved with should be within support).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Oncom
Commander Oncom
Commander

Posted: ‎2020-01-28 10:55 PM

In response to Anonymous user
0 Likes
0
6559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-28 10:55 PM

now it works after I restart all PC and still using this configuration from @Anonymous user .

 

Thanks All, @Anonymous user @BevanWeiss @sbeadle 

www.pamtek.co.id
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of