Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-17 02:31 PM
Hi, Looking for advice please,
New to GeoScada although have used many different packages (Ignition, FTV, Citect etc) and latest project is GeoScada to Omron NX1 series PLCs over Ethernet/IP. Thought it would just be a case of setting up a PLC direct or outstation channel Ethernet/IP in ViewX. Not so I'm thinking now.
Looking for any advice or similar setups please..starting to think I will need a 3rd party software WOW,
Help
thanks in advance
Clive
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-29 07:35 AM
The Ethernet/IP driver is targeted specifically for AB devices.
You may be better off using the OPC UA driver.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-29 07:35 AM
The Ethernet/IP driver is targeted specifically for AB devices.
You may be better off using the OPC UA driver.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-02 06:01 PM
Thanks, yes will be using Kepware and OPC UA
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.