Hi, Looking for advice please,
New to GeoScada although have used many different packages (Ignition, FTV, Citect etc) and latest project is GeoScada to Omron NX1 series PLCs over Ethernet/IP. Thought it would just be a case of setting up a PLC direct or outstation channel Ethernet/IP in ViewX. Not so I'm thinking now.
Looking for any advice or similar setups please..starting to think I will need a 3rd party software WOW,
Help
thanks in advance
Clive
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-29 07:35 AM
The Ethernet/IP driver is targeted specifically for AB devices.
You may be better off using the OPC UA driver.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-29 07:35 AM
The Ethernet/IP driver is targeted specifically for AB devices.
You may be better off using the OPC UA driver.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-02 06:01 PM
Thanks, yes will be using Kepware and OPC UA