OPC UA node-red connection

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • OPC UA node-red connection
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
308
AndrewScott
Admiral AndrewScott
96
BevanWeiss
Spock BevanWeiss
91
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
37
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2024-01-30 08:49 AM . Last Modified: ‎2024-01-30 08:50 AM

0 Likes
12
1757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-30 08:49 AM . Last Modified: ‎2024-01-30 08:50 AM

OPC UA node-red connection

Hello everybody!! I´m trying to connect my OPC UA client (node-red) to my server (Geo SCADA), now I'm reading the value from different analog points and the state of some boolean points. But when I try to write any value on the analog points or even when I tried to change the state on any boolean point it's not working, the value/state doesn't change. All the points I'm working with are internal points.

 

Any suggestion?

Labels
  • Labels:
  • SCADA
  • Telemetry
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-11 08:54 AM

0 Likes
1
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 08:54 AM

The super user is only intended to be used to do the initial system setup after which is should be disabled, see Super User Account in the help.

 

However, I'm able write a property using the super user account from Matrikon OPC UA Explorer providing it is running on the same machine as the Geo SCADA server. The super user cannot be used remotely.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-07-08 03:58 AM

0 Likes
0
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-08 03:58 AM

I see no reason why this should not work, except ... security, permissions etc?

Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2024-07-09 06:09 AM

0 Likes
0
1545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-09 06:09 AM

Hi Steve,

 

where can I check those permissions? I used prosys OPC UA browser to connect to geo scada opc server and I noticed the variables that I try to write has only read permissions.

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-10 07:08 AM

0 Likes
0
1542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-10 07:08 AM

For internal points you need to write to the CurrentValue property of the point and your user account needs have Control permission on the points (see Allocating Security Permissions).

 

I'm able to write to internal points using Matrikon OPC UA Explorer successfully.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2024-07-11 08:13 AM

0 Likes
0
1523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 08:13 AM

Hi Andrew, I'm using the super user account to write in the current value property, do I need to use other account??

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2024-07-11 08:54 AM

0 Likes
1
1521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 08:54 AM

The super user is only intended to be used to do the initial system setup after which is should be disabled, see Super User Account in the help.

 

However, I'm able write a property using the super user account from Matrikon OPC UA Explorer providing it is running on the same machine as the Geo SCADA server. The super user cannot be used remotely.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2024-11-18 07:07 AM

In response to AndrewScott
0 Likes
0
1116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-18 07:07 AM

Hello Andrew!

 

I made some tests using PROSYS OPC UA Browser, I tried with different users and the result is the same (image attached).  All the fields of the variables show "[current read]" as permission.  Any suggestion??

 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-11-20 03:01 AM

0 Likes
1
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-20 03:01 AM

Check the type of the point. You can write to the current value of an Internal point, not a protocol (OPC or Modbus) point. 

Check the user account has "Control" permission on your Internal point.

Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2024-11-20 05:25 AM

In response to sbeadle
0 Likes
0
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-20 05:25 AM

Hi Steve! the points is an internal point (analog point), I'm trying to write the current value but it doesn't allow me.  The geoscada user that I'm using has contol and read permissions, but I can only read data.  If you want I can send you the flow (node red) that I'm using, so you can test it. 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-11-22 12:32 AM

0 Likes
1
1091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-22 12:32 AM

Use the Geo SCADA OPC Driver to test controls first. If that works, Node Red is the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2024-11-22 10:44 AM

In response to sbeadle
0 Likes
0
1049
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-22 10:44 AM

Hi Steve, I followed your advise and I tried to write the current status for an internal digital point (boolean) from an OPC digital point, the two points are located in the same viewx, but I got this message (image attached). Any suggestion?

 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2024-11-26 02:05 AM

0 Likes
0
1038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-26 02:05 AM

Goes back to Andrew's comment:

"For internal points you need to write to the CurrentValue property of the point and your user account needs have Control permission on the points (see Allocating Security Permissions).

I'm able to write to internal points using Matrikon OPC UA Explorer successfully."

 

Check server settings:

sbeadle_0-1732615367616.png

 

Check your point's security settings:

sbeadle_1-1732615468345.png

Check the UA user/password (which is a Geo SCADA User/Password) has "Control" privileges in its group.

Reply

Link copied. Please paste this link to share this article on your social media post.

Fernando84
Lieutenant JG Fernando84
Lieutenant JG

Posted: ‎2024-11-26 07:46 AM

0 Likes
0
1015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-26 07:46 AM

Hi Steve!! everything in the geo scada (permissions) was fine, the problem was the user authentication on the OPC server, I fixed it and now it's working good.  Thank you!

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of