Hi,
I'm trying to retrieve Historical Data from Geoscada to Pi using OPC-UA
I tried to connect with OPC UA Server Simulator and the Historical Data folder structure is available for me to browse any tags that are historized
I tried to connect Geoscada OPC UA server and the Historical Data folder is not available even though I enable Historic in all my tags
Can Geoscada OPC UA server expose Historical Data to its Client?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-23 12:09 AM
Hi. Geo SCADA's OPC UA server does not support historic data.
If you want to export Geo SCADA data to PI, you can use OPC-HDA, or use the native PI data feed feature in Geo SCADA 2023.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-23 12:09 AM
Hi. Geo SCADA's OPC UA server does not support historic data.
If you want to export Geo SCADA data to PI, you can use OPC-HDA, or use the native PI data feed feature in Geo SCADA 2023.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.