Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-23 11:26 PM . Last Modified: 2023-05-02 11:51 PM
Dears
I am using Clear SCADA and Sofrel Data loggers. For this i used Simple OPC Server to collect the information from Data loggers. I am facing this issue that if i configure Read Mode as Asynchronized then i found the difference between Current Value and Histories' Value. And Current Value updating on time.
I cross check through OFS Client and found both Value and HValue have same values on their register.
Then i configured Read mode as Synchronize then i found that HValue and Values are the same but not updating once value will change. And there is a Lag of 2 days in updating.
Is there any way to refresh the server on specific time to collect the information ? Or how can be solve this issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-28 05:22 AM . Last Modified: 2022-10-28 08:24 AM
Can you explain what you mean by "Histories' Values"?
The OPC DA standard only deals with current data, not historical data.
Is this some special feature of the Sofrel data logger?
In asynchronous mode the OPC DA client (Geo SCADA) subscribes to updates from the OPC DA server (Sofrel). It's up to the server (Sofrel) to then push changes to the client (Geo SCADA) as they occur. This is the most efficient mode.
In synchronous mode the OPC DA client (Geo SCADA) periodically polls the OPC DA server (Sofrel) to get data. The "Scan Rate" and "Scan Offset" settings on the scanner define when the polls occur. See Configure the Scanner Properties
NB. The Geo SCADA simple OPC driver is a legacy driver for backwards compatibility. The advanced OPC driver should be preferred for all new systems.