Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Modbus Advanced Outstations

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Modbus Advanced Outstations
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
bwill1177
Ensign bwill1177
Ensign

Posted: ‎2023-03-03 01:49 PM . Last Modified: ‎2023-05-02 11:47 PM

0 Likes
8
2804
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-03 01:49 PM . Last Modified: ‎2023-05-02 11:47 PM

Modbus Advanced Outstations

Is there a way to create multiple Modbus TCP Advanced Outstations with the same Modbus slave address but different IP addresses?  My setup is a single Modbus TCP Channel and a single Mdobus Outstation Set.  When I try to add devices with Modbus address 1 and different IP addresses I get an error that I cannot have duplicate Modbus addresses. It seems to me that the check for duplicate addresses should be IP + Modbus address, not just Modbus address.  Is there any way around this?

 

Any help would be greatly appreciated.

Labels
  • Labels:
  • Drivers
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2023-11-02 06:04 AM

0 Likes
0
2287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-02 06:04 AM

When using the Modbus TCP protocol the "Unique Modbus Addressing" setting on the outstation set defines whether or not the Modbus addresses of the outstations within the set must be unique, see Specify Whether a Set Uses Unique Modbus Addressing.

When this setting is disabled, the address must still be unique for each IP address.


Andrew Scott, R&D Principal Technologist, AVEVA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Khaled_Hamed
Crewman Khaled_Hamed Crewman
Crewman

Posted: ‎2023-03-04 02:16 AM

0 Likes
2
2798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-04 02:16 AM

Hello Bwill,

On same serial link you definitely cannot have duplicate slave modbus IDs.

When you say different IP addresses I can assume you have gateway for each slave device, and that shall work. Please let me know more details of the system, that controlled and the devices you are using to be able to help you more.

Reply

Link copied. Please paste this link to share this article on your social media post.

bwill1177
Ensign bwill1177
Ensign

Posted: ‎2023-03-06 05:25 AM

In response to Khaled_Hamed
0 Likes
1
2789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-06 05:25 AM

Hi Khaled,

 

I'm attempting to configure multiple Modbus devices using the Modbus TCP protocol, not serial.  These devices are all uniquely addressed via IP address, however, most of them have a default Modbus address of 1.  When I attempt to configure them in GeoSCADA, I get an error that they cannot have the same Modbus address, even though they have unique IP addresses. 

 

These devices are a mix of power quality meters, pump protection relays, and others. They are currently communicating to an existing SCADA system (not GeoSCADA).  We are migrating to GeoSCADA and thus need to figure out how to configure them to work with the Modbus - Advanced driver.  Thanks for your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

kjwageto
Crewman kjwageto
Crewman

Posted: ‎2023-03-15 10:12 AM

In response to bwill1177
0 Likes
0
2754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-15 10:12 AM

Here's a few settings to check/try:

  1. On the Modbus - Advanced Direct Outstation Set, 'Modbus' tab:
    • Set Address: Make sure it's a unique address and NOT set to '1'
  2. On the Modbus - Advanced Direct Channel, 'Connection' tab:
    • Connection Type: Network
    • TCP/IP Type: TCP
    • Merge Connections: Checked
    • Independent Connections: Checked
Reply

Link copied. Please paste this link to share this article on your social media post.

Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2023-06-05 07:57 AM

0 Likes
0
2671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-05 07:57 AM

Hello Support,

 

I am trying to configure a device though modbus outstation, modbus set and modbus channel. My outstation is showing Healthy Multidrop but my channel is showing disconnected. I have tried different configurations on the channel and no luck getting the channel to connect. My current setting for channel are:

 

Connection Tab:                                             

Network

TCP

Merge Connections unchecked

Independent connections checked.

 

Modbus Tab:

Protocal type: RTU

 

Scan Parameters:

Line speed: 19200

 

Thanks. 

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2023-06-05 01:50 PM

0 Likes
1
2666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-05 01:50 PM

@Rich-CI would start a new post with your question and give some more detail. There are a few types of outstations and channels you can select so it might be that one or both of that you selected aren't really the ones you want. Right click on them and select View to see the type.

Reply

Link copied. Please paste this link to share this article on your social media post.

Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2023-06-06 08:01 AM

In response to geoffpatton
0 Likes
0
2646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-06 08:01 AM

Ok I will start a new post thanks. Will update question with more detail. 

Reply

Link copied. Please paste this link to share this article on your social media post.

TAS1
Crewman TAS1
Crewman

Posted: ‎2023-11-02 04:38 AM

0 Likes
0
2287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-02 04:38 AM

BWills question was never answered, and I have exactly the same question. 

To clarify, it is the Advanced Modbus "Direct Outstation" Modbus tab, Address Field. 

If the same address is used in more than one "Direct Outstation", even if the IP address is different, the outstation will go to error and not work.

 

Modbus TCP devices generally use address 1 or 255, and changing is usually not possible. You cannot have a unique address for every outstation.

 

Schneider have broken the simple Modbus driver (performance is extremely bad) and recommend everyone use the advanced modbus driver, but with this address limitation, it is unusable for multiple modbus outstations.

 

Is this maybe a problem with just this version (2021). 

 

Please can somebody clear up this issue? I must be missing something.

Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2023-11-02 06:04 AM

0 Likes
0
2288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-02 06:04 AM

When using the Modbus TCP protocol the "Unique Modbus Addressing" setting on the outstation set defines whether or not the Modbus addresses of the outstations within the set must be unique, see Specify Whether a Set Uses Unique Modbus Addressing.

When this setting is disabled, the address must still be unique for each IP address.


Andrew Scott, R&D Principal Technologist, AVEVA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore